Simulate almost-full semis/lorries were used as design fires
for the European Runehamar tunnel fire tests in Norway.
It was surprising that solid commodity (mix of
plastic and wood) could create a fire of 200 MW.
200 MW fire is equivalent to a constrained pool fire
(or pool fire with liquid deeper than 2 mm) of
gasoline that is more than 10 yards across with
intermittent flames to 35 ft in the air.
There are caveats:
Fire growth is initially slow inside trailers,
Fire ignition is rare inside trailers,
most semi (heavy goods vehicles) fires start in the
rear of rigs with a brake failure and overheating, or
up front in the engine compartment/driving cab.
Fires were burned on open steel racks to simulate the elevation of
the trailer, only there were no trailer enclosure
Fire load was not representative of worse-case loads
Ventilation, fans, open doors with wind --> will obviously
decrease fire duration and time to full-involvment while
increasing peak HRR.
These have the potential to be big fires-- that fortunately don't
happen all *too* often,
accidentally, in vehicles parked in non-public occupancies.
scot deal
excelsior fire
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)