Impairments are also covered in #25, but it's something you can reference,
excerpt and forward to the OWNER to implement- we have enough risk in this
business.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Johnston
Sent: Wednesday, January 13, 2010 11:42 AM
To: [email protected]
Subject: RE: Cure times

I have always made the owner take care of this procedure, I just give him or
her the information and let them run with it.

Jim Johnston


-----Original Message-----
From: Forest Wilson [mailto:[email protected]] 
Sent: Wednesday, January 13, 2010 8:31 AM
To: [email protected]
Subject: Re: Cure times


But let us remember that Impairment is the owners responsibility and not the
contractors.
Coordinating impairment procedures exposes the contractor to additional
risks.
I would advise the owner to consult the local Fire Marshal.




Forest Wilson 

Project Manager 
Cherokee Fire Protection Co. 
1855 Bellbrook Ave. Ste C
Xenia OH 45385

ph: 937-376-2333 
fx: 614-455-4324 
cell: 937-307-5647 


. 



Visit our blog: www.cherokee-fire.blogspot.com 







NOTICE: The information contained in this email is intended to be solely for
the use of the named individual or entity to which it is directed and may
contain information that is privileged or otherwise confidential. It is not
intended for transmission to, or receipt by, anyone other than the named
addressee (or a person authorized to deliver it to the named addressee). It
should not be copied or forwarded to any unauthorized persons. If you have
received this electronic mail transmission in error, please delete it from
your system without copying or forwarding it, and notify the sender of the
error by reply email or by calling Cherokee Fire Protection Co. at
888-347-3079 toll free.



-----Original Message-----
From: Jim Johnston <[email protected]>
To: [email protected]
Sent: Wed, Jan 13, 2010 11:00 am
Subject: RE: Cure times


Tom,
Not sure what state you are in but if your state utilizes the International
ire Code there is a procedure to follow 2006 IFC 901.7.
Jim Johnston, P.E.
ire Protection Engineer
nland Fire Protection, Inc
100 Ahtanum Road
akima, WA 98903
hone 509-248-4471
ax 509-248-1180
[email protected]

----Original Message-----
rom: Tom Duross [mailto:[email protected]] 
ent: Wednesday, January 13, 2010 4:21 AM
o: [email protected]; [email protected]
ubject: RE: Cure times
So if you're working in an occupied residential bldg. and you have to shut
own a floor for 24 hrs., what precautions to do take?  Or more importantly,
hat approach do you take with regard to impairments to the remainder of the
ccupants and the building?  After explaining why you (not you but all) wait
4 hrs. and the other guy doesn't, and even showing why, assuming they
ecide to go with you, do you have a written impairment plan to follow?  How
o you handle FD concerns?
'm there right now and wondering.
D

 ALWAYS use the 24 hour cure time and maybe longer, depending on
emperature and humidity.

24 hours are required by some of the insurance companies. It is a helpful
ay to mitigate water damage. We observe them. Owner must provide fire
atch.., as required by 101.

hen you look in whichever flavor of CPVC manual you have, be aware of the
emps this time of year. If I am remembering correctly, there is a temp and
ize that you are not allowed to glue at all until the temp in the room is
t that level.
R/
att
_______________________________________________
prinklerforum mailing list
[email protected]
ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
Put the word unsubscribe in the subject field)
_______________________________________________
prinklerforum mailing list
[email protected]
ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to