You can use a loop and no check valve as long as the loop drops 5' and rises to 
no higher than 12" below the supply line (13-2007 figure 7.6.3.1 note 1). Most 
AHJ's will require that there be an RPZ somewhere in the system if any 
contaminant is introduced to the potable water supply (antifreeze)

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jay Jay Blocker
Sent: Tuesday, January 19, 2010 8:23 PM
To: [email protected]
Subject: Antifreeze Backflow Prevention

Using NFPA 13 (2007 thus the reason for my question) I cannot find anything 
saying that using a swing check valve at the end of a wet system and 
transitioning to a glycol system is allowed.  Basically 1 section of a parking 
garage is exposed to cold temps when the garage door opens.  Door failed to 
shut and several freeze breaks happened.  The question has been asked if adding 
a separate control valve before a single check valve at the end of the wet 
system and turning it into antifreeze (without a rpz or a loop) was an 
option.  I don't see where this is an option by  7.6 anywhere.  I feel like I'm 
missing something here.  Are any of the older editions of 13 saying this is 
allowed or am I looking in the wrong spot?
 
J. Blocker
EFPS
(303) 353-9712


      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to