You are undoubtedly correct. Thanks.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Wednesday, January 20, 2010 1:47 PM
To: [email protected]
Subject: RE: exterior heads, interior calcs

Greg:

If I don't have to concurrently flow sprinklers above and below a duct or other 
obstruction that's within the same compartment (22.4.4.6.3), why would I have 
to or want to include sprinklers that are outside of the building, unless you 
were calculating a single row of sprinklers under a soffit or mansard or 
similar condition?

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Wednesday, January 20, 2010 11:39 AM
To: [email protected]
Subject: exterior heads, interior calcs

Just curious to all of you who know the stats, etc.

I have a very unusual shaped remote are due to an unusual shaped building and 
or protecting small alcoves for an ice machine, wash down area, small loading 
dock, etc.

Question:  How often do sprinklers activate on both the exterior and interior 
of a noncombustible building? Is it common? Should they be included in the 
interior calcs?

Doesn't kill us either way, but I am curious.

Thanks,

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Tuesday, January 19, 2010 9:34 PM
To: [email protected]
Subject: Re: Antifreeze Backflow Prevention

J.

I believe you need the loop per 13. The testable backflow device, DCVA
or RPBA, would be a health code requirement as administered by the
cross connection specialist for the water purveyor. 13 would then
allow deletion of the loop but require the expansion tank.

On Tue, Jan 19, 2010 at 6:22 PM, Jay Jay Blocker
<[email protected]> wrote:
> Using NFPA 13 (2007 thus the reason for my question) I cannot find anything 
> saying that using a swing check valve at the end of a wet system and 
> transitioning to a glycol system is allowed.  Basically 1 section of a 
> parking garage is exposed to cold temps when the garage door opens.  Door 
> failed to shut and several freeze breaks happened.  The question has been 
> asked if adding a separate control valve before a single check valve at the 
> end of the wet system and turning it into antifreeze (without a rpz or a 
> loop) was an option.  I don't see where this is an option by  
> 7.6 anywhere.  I feel like I'm missing something here.  Are any of the older 
> editions of 13 saying this is allowed or am I looking in the wrong spot?
>
> J. Blocker
> EFPS
> (303) 353-9712
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4791 (20100120) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4791 (20100120) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to