We don't argue the RPZ requirement. We use non-toxic, but certainly have
seen the Prestone jugs in numerous attics left by competitors. So you have
to assume the worst if its your butt they'll sue for the other's later
error.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Thursday, January 21, 2010 3:19 PM
To: [email protected]
Subject: Re: Antifreeze Backflow Prevention

bloody RPZ's have that annoying spitting characteristic too.

As a sidebar, an RPZ is required for protection against toxic  
compounds but even non-toxic chemicals (like propylene glycol) get  
pushed into using it.  SInce an RPZ is for toxic compounds, a cycle or  
two ago I attempted to delete the restriction against ethylene glycol  
when an RPZ is used.  Needless to say, the TC decided not to depend on  
the RPZ that strongly.  To be honest, I didn't do an extensive review  
to see how stringent the IPC is on compounds that actually are toxic  
since I knew it would fly like a lead balloon.

Anyone that plays with systems with nasty compounds that takes water  
from a potable supply, feel free to send me an off-Forum email  
educating me further.

Roland

On Jan 21, 2010, at 11:41 AM, Matt Grise wrote:

> Sorry...unclear wording.
>
> I meant that you could use either:
>
> 1) an RPZ at the riser, and a drilled check valve at the loop
> 2) a double check bfp at the  riser and an RPZ at the loop
>
> We sometimes use the second setup since RPZ's cost so much more than  
> DC BFP's. If the primary riser is 4,6,8" and the antifreeze loop  
> only needs a 1.25" RPZ, it can be less expensive to use 2 bfp's.
>
> Matt Grisé PE*, LEED AP

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to