Sorry...unclear wording.

I meant that you could use either:

1) an RPZ at the riser, and a drilled check valve at the loop
2) a double check bfp at the  riser and an RPZ at the loop

We sometimes use the second setup since RPZ's cost so much more than DC BFP's. 
If the primary riser is 4,6,8" and the antifreeze loop only needs a 1.25" RPZ, 
it can be less expensive to use 2 bfp's.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Thursday, January 21, 2010 1:38 PM
To: [email protected]
Subject: Re: Antifreeze Backflow Prevention

What's your basis for requiring two backflow prevention devices?  You  
can use the U-loop with the drilled check valve on the antifreeze  
system w/o a BFP but then your backflow protection between the  
sprinkler system and the potable water can no longer be just a double  
check BFP but must be a reduced-pressure type.

Roland

On Jan 21, 2010, at 8:25 AM, Matt Grise wrote:

> You are correct. There needs to be backflow protection between the  
> public/domestic supply and the sprinkler system, and  also between  
> the wet system and the antifreeze loop.
>
> Matt Grisé PE*, LEED AP
> Sales Engineer
> Alliance Fire Protection
> *Licensed in KS & MO
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to