I dissent a bit on the hazard and sprinkler design being a building code
issue.  We protect the hazard, period.  Yes, whether it's a B or an M is
considered but it certainly is not the end of the consideration.  How about
a grocery store with HPS around the perimeter or a single aisle?  Ever seen
a 12' high aisle with plastics (paper plates) and encapsulated class III
(toilet paper and paper towels in bulk) in a grocery.  We don't ignore that.
We do ignore minor quantities of things including flammable liquids but I
can't tell you I have a solid code to say how much we can ignore. When the
building code says it's an H then yes we jump. 

But I'd contend whether it's storage or a Sam's we should be treating the
vegetable oil the same as far as sprinkler design.  A single pallet in
either case we can probably ignore.  10 pallets, both should be the same
sprinkler design.  True the building code doesn't treat them the same but
that doesn't mean anything to us again IMHO.  How about a small rack of
tires in a repair garage?  We go to the tire section for storage and the
occupancy is an F or H.   How about a museum with paintings vs. a children's
or science museum?  Both A's one LH and the other OH.  

And as far as out guessing future occupancies I'm just not that good.  All
the salons I've been in are LH IMHO.  In some cases the existing system and
which hazard the base is may not make a difference when changing.  If the
base is BUP shell and they are dropping a new ceiling it can make one hell
of a cost difference to maintain OH when LH is required.  Another case is
when you come to a new wall.  If the OH spacing is 10'x12' and the new wall
is 7.5' from a wall move on in LH.  If you cut in a new head to maintain the
5' or 6' to a wall you might have just added an extra head to the calcs on a
BL.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, January 21, 2010 3:05 PM
To: [email protected]
Subject: RE: Occupancy

If this is a strip shopping center it's in the owner's best interest to
treat the entire shell as Mercantile and be done with it.  That way any
retail or service type business can occupy the space.  If you try to dissect
the categories of the occupants as to whether they may actually be a "B" or
"M" occupancy it will only create problems down the road when the "B"/LH
beauty shop moves out and the "M"/OH Granny's Knick-Knacks and Haberdashery
goes into the space.

And yes, this is a Building Code issue, not an NFPA 13 issue.  The NFPA part
is secondary to the BC issue.

But if the system is existing, leave it alone.  


But personally, shouldn't most beauty salons be considered an "H" occupancy
and protected with foam-water deluge systems, I mean look at the chemical
list, the smells make me think there are some serious toxics
involved..............  ;)


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob Caputo
Sent: Thursday, January 21, 2010 3:44 PM
To: [email protected]
Subject: Occupancy

In my opinion, the question isn't directly an NFPA 13 issue but rather
Building and Fire Code issues in terms of occupancy and allowable amounts of
chemical or hazardous materials within a control area.  Normally, the code
exempts (to a degree) mercantile occupancies where products containing
flammables, combustibles or hazardous materials (irritants, toxics,
carcinogens, etc) are stored in the same containers they are sold in.
That's why Costco, Sams, BJ's and similar can store more vegetable oils in
quantity than a manufacturing or storage use building could have in storage
of a product with the same flash point.

That said, at some point in the process of analysis  someone has to decide
what the corresponding NFPA 13 occupancy use group or commodity and storage
arrangement is, so sprinkler design criteria can be established...   I
suggest this is a job for a consultant or an engineer of record - not the
contractor.  (again - just stating my opinion)


Bob Caputo, CFPS, CET
657 Cantara Lane - Vista, CA 92081

Fire & Life Safety America Company
3017 Vernon Rd - Richmond, VA 23228
Office: (804) 222-1381  Cell: (804) 263-1577
                                         
 


    

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Keith Pepin
Sent: Thursday, January 21, 2010 8:23 AM
To: [email protected]
Subject: Occupancy

I am working on a project that doesn't have an Eng of Record. The building
contains large individual shell spaces. The original sprinkler system was
designed for a mercantile occupancy. A tenant has purchased a couple of
spaces and is opening a beauty/hair salon. I don't see the fuel load as a
normal mercantile occupancy would have. Light or ord. Please comment. 

 

 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to