Aaron, You will probably find that your friendly fire marshal will show you
that his fire code does not recognize a gaseous system as an alternative to
a sprinkler system.  Check with him/her.  Code trumps NFPA standards and
codes,

Also he will be more friendly if you spell his title without the second (L)


Ed Vining

On Tue, Feb 9, 2010 at 10:35 AM, <[email protected]> wrote:

>
> Does anyone know if NFPA specifically states that a gas fire suppression
> system can replace a fire sprinkler in a room, or rooms? I scanned and
> searched and the only section it addresses that issue is in marine systems
> 25.1.5, partial systems. Section 1.5 possibly covers it but convincing a
> fire marshall of that could be a bit tough. Thanks.
>