What we have often seen with these isolated rooms with gaseous protection is
that the AHJ will require that space to have rated construction in addition
to the gaseous system.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Autry, David
Sent: Tuesday, February 09, 2010 2:17 PM
To: [email protected]
Subject: RE: Gas systems replacing sprinklers

Look at NFPA 101 (2000, edition) 9.7.3.1

In any occupancy where the character of the potential fuel for fire is such
that extinguishment or control of fire is effectively accomplished by a type
of automatic extinguishing system other than an automatic sprinkler system,
such as water mist, carbon dioxide, dry chemical, foam, Halon 1301, water
spray, or a standard extinguishing of another type, that system shall be
permitted to be installed in lieu of an automatic sprinkler system. Such
systems shall be installed, inspected, and maintained in accordance with
appropriate NFPA standards.




David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
** Note new email address: [email protected]
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, February 09, 2010 12:35 PM
To: [email protected]
Subject: Gas systems replacing sprinklers


Does anyone know if NFPA specifically states that a gas fire suppression
system can replace a fire sprinkler in a room, or rooms? I scanned and
searched and the only section it addresses that issue is in marine systems
25.1.5, partial systems. Section 1.5 possibly covers it but convincing a
fire marshall of that could be a bit tough. Thanks.

Aaron Johnson
Northwest Consulting, Inc. 



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to