Or gas with spkr (PA?) backup using higher temp heads, or use concealed to
protect against mechanical injury if that's a concern in that environ.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, February 09, 2010 1:49 PM
To: [email protected]
Subject: RE: Gas systems replacing sprinklers

If the facility is required to be "sprinklered throughout" as a Code
requirement, the AHJ would have to approve the removal of a sprinkler system
and substitution of a gaseous system.  There's nothing in NFPA that gives
unconditional permission to just change things.   Plus functionality of the
systems are completely different so it's hard to compare the two and say
that gas is an equal substitute to automatic sprinklers.  

In A.21.26.1.1 dealing with Cleanrooms, NFPA 13 states, "Gaseous fire
suppression systems are not substitutes for automatic
sprinkler protection. The large number of air changes in cleanrooms can
cause dilution or stratification of the gaseous agent."

That's about all the verbiage you'll get in 13 concerning the gas systems.

Unless there's some real serious concerns over sprinklers you might suggest
going preaction instead of gas.

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, February 09, 2010 1:35 PM
To: [email protected]
Subject: Gas systems replacing sprinklers


Does anyone know if NFPA specifically states that a gas fire suppression
system can replace a fire sprinkler in a room, or rooms? I scanned and
searched and the only section it addresses that issue is in marine systems
25.1.5, partial systems. Section 1.5 possibly covers it but convincing a
fire marshall of that could be a bit tough. Thanks.

Aaron Johnson
Northwest Consulting, Inc. 



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to