Mike, go to www.apsonline.com/gasket.html.I think this is what you are looking 
for.


---- [email protected] wrote: 
> 
> All: 
> 
> I've had opportunity to use install these in the pulp industry in another 
> life, and have seen them in my current place. I assume Steve is describing a 
> set up like this: 
> 
> Flange by Flange ftg. 
> 
> Drop bolts in first to ensure its ready. 
> 
> Clean flange, and tools, then hands. We used acetone from the lab to clean 
> our wrenches. Now I know it does burn. Not a good idea. Then rubber (probably 
> some kind of plastic) gloves. 
> 
> Bolts, flange, and steel washers are normal. If bolts are barely long enough 
> with normal washers, go up one length. 
> 
> Special non-conductive gaskets, and washers are used to provide the 
> isolation. But the real parts that take a little messing with are the sleeves 
> that go around the bolts. The need to be just shorter than the distance 
> between the faces of the flanges after makeup. We always had another fitter, 
> and the operator check them afterwords. This is not a place to try to be 
> productive. 100% was the only acceptable level. The operator had to check 
> something off some form or report. The goal was to prevent the adjacent tank 
> from exploding. 
> 
> Then make sure you get something on the wrenches so the don't rust. 
> 
> 
> Yours, 
> 
> Bruce V. 
> 
> 
> 
> ----- Original Message ----- 
> From: "steve" <[email protected]> 
> To: "AFSA" <[email protected]> 
> Sent: Friday, March 5, 2010 8:29:23 AM GMT -08:00 US/Canada Pacific 
> Subject: Re: "SCIF" Wall Penetration 
> 
> Is this at the service entry? You can use a dielectric flange kit at that 
> point or, as Geo said a dielectric union. 
> 
> SL 
> 
> 
> ------Original Message------ 
> From: Mike Brown 
> Sender: [email protected] 
> To: AFSA 
> ReplyTo: AFSA 
> Subject: "SCIF" Wall Penetration 
> Sent: Mar 5, 2010 4:15 AM 
> 
> Question I am working on a project where the FPE is asking for a 
> "electrically isolated joint on the sprinkler feed main just inside the 
> wall"? Has anyone had to deal with this before...if so what did you use? 4" 
> Sch. 40 Main. 
> Thanks, 
> Mike Brown 
> _______________________________________________ 
> Sprinklerforum mailing list 
> [email protected] 
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
> 
> For Technical Assistance, send an email to: [email protected] 
> 
> To Unsubscribe, send an email to:[email protected] 
> (Put the word unsubscribe in the subject field) 
> 
> 
> Sent from my Verizon Wireless BlackBerry 
> _______________________________________________ 
> Sprinklerforum mailing list 
> [email protected] 
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
> 
> For Technical Assistance, send an email to: [email protected] 
> 
> To Unsubscribe, send an email to:[email protected] 
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to