I think it's ambiguous because it is ambiguous. I wouldn't have a bit
of trouble worrying about black piper exposed to weather in Arizona or
Saudi Arabia. Might get a surface rusting but that's protective. I
might, on the other hand, be horrified of the thought of using
anything but that stuff that has the zinc impregnated into the outer
layers of the steel rather than as just a coating (don't want to name
it and be accused of advertising a product) on a North Sea offshore
oil platform, even for inside stuff. All is situational.

On Wed, Mar 17, 2010 at 11:38 AM, Bobby Gillett
<[email protected]> wrote:
> I was in FL at one time a few years ago, could be the same one.
>
> Not the same, but still good.
>
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office  (731) 424-9285 fax
> (731) 267-4853 cell
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Chris Cahill
> Sent: Wednesday, March 17, 2010 1:35 PM
> To: [email protected]
> Subject: RE: Exterior dry system piping under canopy
>
> Oooops, nah, it's all different if it's not here.  I have to drive through
> TN next month to get to FL. It's not all the same "down there", lol.
>
> Must be the other Bobby, yeah that's my story.
>
> Chris
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Bobby Gillett
> Sent: Wednesday, March 17, 2010 1:29 PM
> To: [email protected]
> Subject: RE: Exterior dry system piping under canopy
>
> No no, Bobby is in TN. and this is a fully covered canopy. - beam & purlin
> construction.
>
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office  (731) 424-9285 fax
> (731) 267-4853 cell
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Chris Cahill
> Sent: Wednesday, March 17, 2010 1:26 PM
> To: [email protected]
> Subject: RE: Exterior dry system piping under canopy
>
> I don't see it as that clear.  '02-8.15.3.2.3 Where corrosive conditions
> exist OR the piping is exposed to weather......
>
> So I guess it depends on the definition of "exposed to weather".  One could
> say outside period.  Bobby is in FL, I imagine ambient air is a little
> moister and perhaps saltier even inland than here in the flooded tundra.
>
> Or I guess it could mean gets rained on so with a cover maybe not exposed to
> weather.
>
> I know open parking ramps don't fair well here with black nor do wash bays
> inside.  Generic store front canopy a little grayer.
>
> Chris Cahill, P.E.
> Fire Protection Engineer
> Sentry Fire Protection, Inc.
>
> 763-658-4483
> 763-658-4921 fax
>
> Email: [email protected]
>
> Mail: P.O. Box 69
>        Waverly, MN 55390
>
> Location: 4439 Hwy 12 SW
>              Waverly, MN 55390
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of John Denhardt
> Sent: Wednesday, March 17, 2010 12:39 PM
> To: [email protected]
> Subject: RE: Exterior dry system piping under canopy
>
> It is not required to be galvanized per NFPA 13.
>
> John
>
>
> John August Denhardt, P.E.
> Strickland Fire Protection Incorporated
> 5113 Berwyn Road
> College Park, Maryland 20740
> Office Telephone Number:  301-474-1136
> Mobile Telephone Number:  301-343-1457
> FIRE SPRINKLERS SAVE LIVES
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Bobby
> Gillett
> Sent: Wednesday, March 17, 2010 1:44 PM
> To: [email protected]
> Subject: Exterior dry system piping under canopy
>
> I have a dry system (non-FM in TN) under an exterior canopy. Is there
> somewhere it states the pipe and fittings are to be corrosion resistant
> (ex.
> Galv.)? I thought somewhere it stated for preact it had to be
> regardless,
> but I can't find that either. Maybe I'm pulling an old spec from a
> project
> out of my brain as the last two I've done have required galv. piping per
> the
> spec book.
>
>
>
>
>
> Bobby Gillett
>
> Sr. Project Manager
>
> Key Fire Protection, Inc.
>
> (731) 424-0130 office  (731) 424-9285 fax
>
> (731) 267-4853 cell
>
>  <mailto:[email protected]>
> [email protected]
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com
> Version: 9.0.791 / Virus Database: 271.1.1/2752 - Release Date: 03/17/10
> 02:33:00
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com
> Version: 9.0.791 / Virus Database: 271.1.1/2752 - Release Date: 03/17/10
> 02:33:00
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to