Ah yes and when they set outside for a while they eventually start to form rust 
on them. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Wednesday, March 17, 2010 4:06 PM
To: [email protected]
Subject: Re: Exterior dry system piping under canopy

Black pipe has a protective coating and the more expensive seems to have a 
better coating. These are usually of a varnish type. Remember that those slings 
of Hyundai black steel 53 & 54 came here on a boat.

On Wed, Mar 17, 2010 at 12:13 PM,  <[email protected]> wrote:
> The appendix of 13 (A.8.16.4.2.1) does give some commentary for 
> certain conditions where "If corrosive conditions are not of great intensity 
> and humidity is not abnormally high, good results can be obtained by a 
> protective coating of red lead and varnish or by a good grade of commercial 
> acid-resisting paint. The paint manufacturer's instructions should be 
> followed in the preparation of the surface and in the method of application."
>
> But the point being that pipe exposed to the weather is to have some sort of 
> protection.  If you take this literally it appears to leave no option for 
> non-protected black steel pipe in exposed conditions.
>
>
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax - 
> 864.599.8439 [email protected] http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of John 
> Denhardt
> Sent: Wednesday, March 17, 2010 2:44 PM
> To: [email protected]
> Subject: RE: Exterior dry system piping under canopy
>
> I agree with Ron.  Just because it is outside under a canopy would not mean 
> it has to be galvanized.  I think a lot has to be where the building is 
> located.  I would be perfectly happy with a coat of paint on the piping in an 
> area where occasionally the pipe might be exposed to the elements.
>
>
> John
>
> John August Denhardt, P.E.
> Strickland Fire Protection Incorporated
> 5113 Berwyn Road
> College Park, Maryland 20740
> Office Telephone Number:  301-474-1136 Mobile Telephone Number:  
> 301-343-1457 FIRE SPRINKLERS SAVE LIVES
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ron 
> Greenman
> Sent: Wednesday, March 17, 2010 2:49 PM
> To: [email protected]
> Subject: Re: Exterior dry system piping under canopy
>
> I think it's ambiguous because it is ambiguous. I wouldn't have a bit of 
> trouble worrying about black piper exposed to weather in Arizona or Saudi 
> Arabia. Might get a surface rusting but that's protective. I might, on the 
> other hand, be horrified of the thought of using anything but that stuff that 
> has the zinc impregnated into the outer layers of the steel rather than as 
> just a coating (don't want to name it and be accused of advertising a 
> product) on a North Sea offshore oil platform, even for inside stuff. All is 
> situational.
>
> On Wed, Mar 17, 2010 at 11:38 AM, Bobby Gillett 
> <[email protected]> wrote:
>> I was in FL at one time a few years ago, could be the same one.
>>
>> Not the same, but still good.
>>
>> Bobby Gillett
>> Sr. Project Manager
>> Key Fire Protection, Inc.
>> (731) 424-0130 office  (731) 424-9285 fax
>> (731) 267-4853 cell
>> [email protected]
>>
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Chris 
>> Cahill
>> Sent: Wednesday, March 17, 2010 1:35 PM
>> To: [email protected]
>> Subject: RE: Exterior dry system piping under canopy
>>
>> Oooops, nah, it's all different if it's not here.  I have to drive 
>> through TN next month to get to FL. It's not all the same "down there", lol.
>>
>> Must be the other Bobby, yeah that's my story.
>>
>> Chris
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Bobby 
>> Gillett
>> Sent: Wednesday, March 17, 2010 1:29 PM
>> To: [email protected]
>> Subject: RE: Exterior dry system piping under canopy
>>
>> No no, Bobby is in TN. and this is a fully covered canopy. - beam & 
>> purlin construction.
>>
>> Bobby Gillett
>> Sr. Project Manager
>> Key Fire Protection, Inc.
>> (731) 424-0130 office  (731) 424-9285 fax
>> (731) 267-4853 cell
>> [email protected]
>>
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Chris 
>> Cahill
>> Sent: Wednesday, March 17, 2010 1:26 PM
>> To: [email protected]
>> Subject: RE: Exterior dry system piping under canopy
>>
>> I don't see it as that clear.  '02-8.15.3.2.3 Where corrosive 
>> conditions exist OR the piping is exposed to weather......
>>
>> So I guess it depends on the definition of "exposed to weather".  One 
>> could say outside period.  Bobby is in FL, I imagine ambient air is a 
>> little moister and perhaps saltier even inland than here in the flooded 
>> tundra.
>>
>> Or I guess it could mean gets rained on so with a cover maybe not 
>> exposed to weather.
>>
>> I know open parking ramps don't fair well here with black nor do wash 
>> bays inside.  Generic store front canopy a little grayer.
>>
>> Chris Cahill, P.E.
>> Fire Protection Engineer
>> Sentry Fire Protection, Inc.
>>
>> 763-658-4483
>> 763-658-4921 fax
>>
>> Email: [email protected]
>>
>> Mail: P.O. Box 69
>>        Waverly, MN 55390
>>
>> Location: 4439 Hwy 12 SW
>>              Waverly, MN 55390
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of John 
>> Denhardt
>> Sent: Wednesday, March 17, 2010 12:39 PM
>> To: [email protected]
>> Subject: RE: Exterior dry system piping under canopy
>>
>> It is not required to be galvanized per NFPA 13.
>>
>> John
>>
>>
>> John August Denhardt, P.E.
>> Strickland Fire Protection Incorporated
>> 5113 Berwyn Road
>> College Park, Maryland 20740
>> Office Telephone Number:  301-474-1136 Mobile Telephone Number:
>> 301-343-1457 FIRE SPRINKLERS SAVE LIVES
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Bobby 
>> Gillett
>> Sent: Wednesday, March 17, 2010 1:44 PM
>> To: [email protected]
>> Subject: Exterior dry system piping under canopy
>>
>> I have a dry system (non-FM in TN) under an exterior canopy. Is there 
>> somewhere it states the pipe and fittings are to be corrosion 
>> resistant (ex.
>> Galv.)? I thought somewhere it stated for preact it had to be 
>> regardless, but I can't find that either. Maybe I'm pulling an old 
>> spec from a project out of my brain as the last two I've done have 
>> required galv. piping per the spec book.
>>
>>
>>
>>
>>
>> Bobby Gillett
>>
>> Sr. Project Manager
>>
>> Key Fire Protection, Inc.
>>
>> (731) 424-0130 office  (731) 424-9285 fax
>>
>> (731) 267-4853 cell
>>
>>  <mailto:[email protected]>
>> [email protected]
>>
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field) 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> No virus found in this incoming message.
>> Checked by AVG - www.avg.com
>> Version: 9.0.791 / Virus Database: 271.1.1/2752 - Release Date:
>> 03/17/10 02:33:00
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> No virus found in this incoming message.
>> Checked by AVG - www.avg.com
>> Version: 9.0.791 / Virus Database: 271.1.1/2752 - Release Date:
>> 03/17/10 02:33:00
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to