Nitrogen works fine as long as the maintenance guy understands the
nitrogen cylinder is just like the compressor tank with the automatic
refill feature (the compressor) shut-off. Too many building folks and
even fitters don't see the correlation (like the mechanic that doesn't
understand the Ford starter solenoid is just like the everybody else's
but in a different place) between one form of gaseous maintenance and
another. Maybe it's the language. Air is something you "make" with a
compressor machine and nitrogen comes from the gas supplier like
acetylene. Obviously something completely different and sprinklers
have AIR maintenance devices. Special gas maintenance MUST be
something different. And if I remember my gas laws correctly different
molecules would be excited to a different degree relative to an equal
pressure so that even something like mercury vapor at X psi would be
exerting the same force at a potential leak site as nitrogen at the
same pressure. Of course getting mercury to vaporize might require
pressures that would change nitrogen to a liquid state but that's way
beyond my 7 AM/40 year ago basic college science knowledge.

On Fri, Mar 26, 2010 at 6:48 AM, Chris Cahill <[email protected]> wrote:
> I was under the impression we talked about nitrogen in dry systems was a
> challenge because it leaked where plain air would not.  I searched the last
> few years of the forum and couldn't find any such discussion.  But air is
> 80% nitrogen so maybe not a significant difference?  How many of you have
> tried nitrogen and did you or do you still have leaking problems?
>
>
>
> Chris Cahill, P.E.
>
> Fire Protection Engineer
>
> Sentry Fire Protection, Inc.
>
>
>
> 763-658-4483
>
> 763-658-4921 fax
>
>
>
> Email: [email protected]
>
>
>
> Mail: P.O. Box 69
>
>        Waverly, MN 55390
>
>
>
> Location: 4439 Hwy 12 SW
>
>              Waverly, MN 55390
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to