A relatively simple solution that is less costly than a connected reserve
bottle of N2 is to have an ASME pressure vessel with air or nitrogen as a
smaller capacity connected reserve; when the low air switch goes off because
the N2 tank is empty, you close the valve and install the protective cap
atop the N2 bottle and get it refilled; open the valve from the little tank
of air or nitrogen and you've got the interim supply until the gas supplier
shows up with the new tank, or the maintenance guy gets tired of hearing the
bottle roll around in the back of his pickup and gets it refilled and
re-installed.

And chris- isn't Air comprised of 72% N2, 22% O2, and the balance a mix of
rare gases, smog, and the stench of NAHB propaganda?

>From Wiki: Dry air contains roughly (by volume) 78% nitrogen, 21% oxygen,
0.93% argon, 0.038% carbon dioxide, and small amounts of other gases. Air
also contains a variable amount of water vapor, on average around 1%.

Ok, Chris was closer and I owe him a beer next time I go ice fishing. Fitter
training session going on today in Minneapolis, in case you didn't know what
the non-signatory guys were up to today. Small industry, eh?

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Scott A.
Futrell
Sent: Friday, March 26, 2010 10:15 AM
To: [email protected]
Subject: RE: Nitrogen

Chris,

I've used and specified nitrogen without problems especially as a backup
for dry and special hazard systems.  Agree with Ron that the biggest
problem is making sure the cylinders are replaced.
John D. provided some information on nitrogen generation systems (that
are spendy), but yet another option.

Scott Futrell
 
(763) 425-1001 Office
(612) 759-5556 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Friday, March 26, 2010 8:48 AM
To: [email protected]
Subject: Nitrogen

I was under the impression we talked about nitrogen in dry systems was a
challenge because it leaked where plain air would not.  I searched the
last
few years of the forum and couldn't find any such discussion.  But air
is
80% nitrogen so maybe not a significant difference?  How many of you
have
tried nitrogen and did you or do you still have leaking problems?  

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [email protected]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to