Chris, I believe nitrogen is no more likely to leak than air (or not
significantly so).  What comes into play is the utmost importance of
installing a very tight sprinkler system, including grooved couplings listed
for dry service.  The owner generally won't complain if the air compressor
runs more than it should, but when he's replacing a N bottle once/week or
more often, he can turn grumpy.

Ed Kramer

> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of Chris Cahill
> Sent: Friday, March 26, 2010 7:48 AM
> To: [email protected]
> Subject: Nitrogen
> 
> I was under the impression we talked about nitrogen in dry systems was a
> challenge because it leaked where plain air would not.  I searched the
> last
> few years of the forum and couldn't find any such discussion.  But air
> is
> 80% nitrogen so maybe not a significant difference?  How many of you
> have
> tried nitrogen and did you or do you still have leaking problems?
> 
> 
> 
> Chris Cahill, P.E.
> 
> Fire Protection Engineer
> 
> Sentry Fire Protection, Inc.
> 
> 
> 
> 763-658-4483
> 
> 763-658-4921 fax
> 
> 
> 
> Email: [email protected]
> 
> 
> 
> Mail: P.O. Box 69
> 
>         Waverly, MN 55390
> 
> 
> 
> Location: 4439 Hwy 12 SW
> 
>               Waverly, MN 55390
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to