WHat does when the FD draws water or how much have do with this  
discussion?  You are confusing reality with the explicit methodology  
of 13.  The standard provides repeatability - period.  The only thing  
it has to do with reality is THAT IT WORKS.  This applies not just to  
this question but basically EVERYTHING regarding hydraulic design.   
Maybe it falls under quantum mechanics.

Roland

On May 9, 2010, at 12:10 PM, A.P.Silva wrote:

>
> When sizing a water tank,
>
> OH design requires 60 to 90 minute water supply for sprinklers
>
> Is 250 gpm outside hose allowance also 60 to 90 minutes?
>
> It seems to me they are both independent requirements. There will be  
> a time
> lag between the two and the fire department could be drawing out  
> more than
> the 250 gpm, for a longer or shorter duration. The question is will  
> the
> intent of the code be satisfied if the total water requirements  
> (sprinklers
> and hose allowances) be supplied for 60 to 90 minutes?
>
> Tony
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to