A-ha! What Roland said. If you think about it, putting that in there in the first place didn't make sense. If we don't have to consider sprinklers and standpipes concurrently in sizing the water supply capacity, why would we calculate them that way? It's not congruent. Once the Class I standpipe is put to use, the functionality of the sprinkler system becomes secondary to the firefighting operation and the safety of responders. Plus, you've got another water supply connected through the FDC so the automatic one on which the calc's were based isn't the only criterion after that.
Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Thursday, April 08, 2010 2:47 PM To: [email protected] Subject: RE: Water Supply Where is that stated Steve, And where is that NFPA 13 A.11.2.3.1.8 (9) come from, I can't find it. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: April 8, 2010 3:12 PM To: [email protected] Subject: RE: Water Supply Inside hose allowance is for cabinets, NOT a Class I standpipe system. A common misapplication ... Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of A.P.Silva Sent: Sunday, May 09, 2010 1:10 PM To: [email protected] Subject: RE: Water Supply NFPA 13, 2007 section A.11.2.3.1.8 (9). Doesn't it appear to require inside hose allowance to be added to the sprinkler demand at the point of connection? Tony -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Roland Huggins Sent: April 8, 2010 2:39 PM To: [email protected] Subject: Re: Water Supply WHat does the presence of the 2-1/2 have to do with this issue (unless you are supply the standpipe supply per 14)? The sprinkler calc does not include an inside hose demand for hose connections on a standpipe. Roland On May 9, 2010, at 12:31 PM, A.P.Silva wrote: > The building code here says the water supply need not satisfy the IFC > fire flow if the building is sprinklered. There will also be > standpipes in the building with 2 1/2" hose valves. > > Tony > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 4946 (20100315) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __________ Information from ESET NOD32 Antivirus, version of virus signature database 4946 (20100315) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 4946 (20100315) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __________ Information from ESET NOD32 Antivirus, version of virus signature database 4946 (20100315) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)