That reference is for the 02 edition.  It moved to 11.1.5.6 in the 07  
edition where the Annex did indeed say -  add 50 gpm per hose  
connection up to 100 gpm for the 2-1/2 connection.  In the 2010 ed we  
corrected that mis-statement and in A.11.1.6.6 (yea it moved from .5  
to .6) that portion of the sentence was intentionally deleted.

So why would that cause any confusion in the industry? - lol

Roland

On May 9, 2010, at 1:10 PM, A.P.Silva wrote:

> NFPA 13, 2007 section A.11.2.3.1.8 (9). Doesn't it appear to require  
> inside
> hose allowance to be added to the sprinkler demand at the point of
> connection?
>
> Tony