That reference is for the 02 edition. It moved to 11.1.5.6 in the 07 edition where the Annex did indeed say - add 50 gpm per hose connection up to 100 gpm for the 2-1/2 connection. In the 2010 ed we corrected that mis-statement and in A.11.1.6.6 (yea it moved from .5 to .6) that portion of the sentence was intentionally deleted.
So why would that cause any confusion in the industry? - lol Roland On May 9, 2010, at 1:10 PM, A.P.Silva wrote: > NFPA 13, 2007 section A.11.2.3.1.8 (9). Doesn't it appear to require > inside > hose allowance to be added to the sprinkler demand at the point of > connection? > > Tony _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)