Tony, It sounds like this is the ONLY water supply to this building.It may be prudent to consider this in your design as the only additional water the fire dept. will have is what they bring on the pumper truck.Once you have the cost of a tank in the job,it may be a small price to upsize it as compared to the value of lives,building,etc.I would go with the MOST demanding for 90 min. (maybe even 120 min) just to be on the safe side.JMHO.
Lamar Vaughn , SET > > > >> > >> When sizing a water tank, > >> > >> OH design requires 60 to 90 minute water supply for sprinklers > >> > >> Is 250 gpm outside hose allowance also 60 to 90 minutes? > >> > >> It seems to me they are both independent requirements. There will be > >> a time > >> lag between the two and the fire department could be drawing out > >> more than > >> the 250 gpm, for a longer or shorter duration. The question is will > >> the > >> intent of the code be satisfied if the total water requirements > >> (sprinklers > >> and hose allowances) be supplied for 60 to 90 minutes? > >> > >> Tony > >> > >> _______________________________________________ > >> Sprinklerforum mailing list > >> [email protected] > >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >> > >> For Technical Assistance, send an email to: [email protected] > >> > >> To Unsubscribe, send an email to:Sprinklerforum- > >> [email protected] > >> (Put the word unsubscribe in the subject field) > >> > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > For Technical Assistance, send an email to: [email protected] > > > > To Unsubscribe, send an email to:Sprinklerforum- > > [email protected] > > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)