It is a 4 storey sprinklered building with a standpipe as per NFPA 14. The
standpipe is manual with the FD pumping into the standpipe system. That is
why I thought to size the tank for additional 250 gpm, so FD will have
enough. 13, 2007 table 11.2.3.1.1 seems to indicate 60 to 90 minutes for
hose allowances also. Is that how you would read? 

Tony   

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: April 8, 2010 2:43 PM
To: [email protected]
Subject: RE: Water Supply

Is it a high-rise building with a 30 minute automatic water supply?   Or
is it a low-rise or mid-rise with a manual standpipe system?  If the latter,
where is the water coming from for the FD to pump into the standpipe?

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Sunday, May 09, 2010 12:31 PM
To: [email protected]; [email protected]
Subject: RE: Water Supply

The building code here says the water supply need not satisfy the IFC fire
flow if the building is sprinklered. There will also be standpipes in the
building with 2 1/2" hose valves. 

Tony  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack,
SET
Sent: April 8, 2010 2:17 PM
To: [email protected]
Subject: Re: Water Supply

If there are no hydrants/hose valves downstream of the tank, you don't need
the 250 gpm added.  If there are hydrants downstream of the tank, are you
going to have to meet site fire flow requirements per the IFC?  
If you have to do that, your tank size is going to be huge!

On 5/9/2010 12:10 PM, A.P.Silva wrote:
> When sizing a water tank,
>
> OH design requires 60 to 90 minute water supply for sprinklers
>
> Is 250 gpm outside hose allowance also 60 to 90 minutes?
>
> It seems to me they are both independent requirements. There will be a

> time lag between the two and the fire department could be drawing out 
> more than the 250 gpm, for a longer or shorter duration. The question 
> is will the intent of the code be satisfied if the total water 
> requirements (sprinklers and hose allowances) be supplied for 60 to 90
minutes?
>
> Tony
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>    
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus signature
database 4946 (20100315) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus signature
database 4946 (20100315) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to