Chris:
 
There are UL listed bulkhead fittings or seals that are intended to seal the 
penetrations of pipes into hoods and ducts in kitchen installations.  See NFPA 
96 and UL Directory.  I know that Ansul sells them and maybe makes them.
 
Maybe not your problem, but something to consider is who is going to do the ITM 
on the sprinklers once installled.  Your typical 25 inspection "from the floor" 
is not going to do it and your fire extinguisher contractor who typically does 
the systems in hoods (albeit 17A wet chem systems) is not going to mess with 
sprinklers.  Consequently, there is a high probablity that the sprinkler 
installation will not get any attention until after the fire which burns out of 
control and the finger-pointin' starts in earnest.


Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 



--- On Mon, 5/3/10, Chris Cahill <[email protected]> wrote:


From: Chris Cahill <[email protected]>
Subject: Kitchen Hoods
To: [email protected]
Date: Monday, May 3, 2010, 2:26 PM


Anyone still putting in wet fire sprinklers as opposed to wet chem systems
under kitchen hoods?  And if so would it make a difference if there was a
deep fryer or not? 



Got an engineer that thought sprinklers would be cheaper to use than wet
chem. on a very small hood.  Well after finding a main and a control valve
and flow switch and ITV I doubt it.   No fryer, although I'm told we can
still get EA-1 heads that are still listed, they are listed in my Tyco book.
We haven't done one in at least 10 or 15 years.  My concerns are sealing the
penetrations especially in the duct (I can pipe around the hood w/o
penetrating I guess).  I can get stainless pipe no problem.



Just curious.   



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: [email protected]



Mail: P.O. Box 69

        Waverly, MN 55390



Location: 4439 Hwy 12 SW

              Waverly, MN 55390



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to