Chris, Penetrations of the hood are probably the least of your problems if there is a fryer (but Dave covered that part already). MN allows the use of EA-1's if you can find them. I don't believe they are listed for that use anymore and in the temperature range you need they need to be replaced frequently (annually?). Where have they been stored for years and will that be a problem?
More importantly though, they had a very limited listing for height above a fryer and it was very difficult to install them within their listing anyway.. Not a good idea IMHO. Scott -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Cahill Sent: Monday, May 03, 2010 2:27 PM To: [email protected] Subject: Kitchen Hoods Anyone still putting in wet fire sprinklers as opposed to wet chem systems under kitchen hoods? And if so would it make a difference if there was a deep fryer or not? Got an engineer that thought sprinklers would be cheaper to use than wet chem. on a very small hood. Well after finding a main and a control valve and flow switch and ITV I doubt it. No fryer, although I'm told we can still get EA-1 heads that are still listed, they are listed in my Tyco book. We haven't done one in at least 10 or 15 years. My concerns are sealing the penetrations especially in the duct (I can pipe around the hood w/o penetrating I guess). I can get stainless pipe no problem. Just curious. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)