there was a lot of chatter on this topic by the TC.  At the ROP, it  
was accepted that a water supply curve through the BFP would be  
produced.  That was killed at the ROC.  ALL that is required is to  
EXERCISE the device at the full system demand.  How you "prove" it can  
be done a couple of ways.  Keep in mind that we are NOT attempting to  
be academically precise but looking for a good ball park number since  
we want a REASONABLY assurance that it is opening fully.  A pitot  
reading on the discharge comes to mind.  A known pressure point that  
has been calculated to provide the system demand is a good way  
(especially if that is the process that is used for the original  
submittal).

Roland

On May 11, 2010, at 6:03 AM, Autry, David wrote:

> ""And where in 25 does it
> say I have to prove anything?""
>
>
> NFPA 25 (2002, Edition) 12.6.2.2
> All backflow devices installed in fire protection water supply shall  
> be tested annually at the designed flow rate of the fire protection  
> system, including required hose stream demands.
>
> Somehow you need to "prove" that you're flowing the required demand.  
> I'm pretty sure the only to do that is measure the flow.
>
>
> David Autry