Careful now, I own a 1981 AMC Concord Wagon with wood siding (among other things). But no leisure suits. Wonder where did I put that Nehru shirt though............. <wink>
Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Wednesday, May 19, 2010 10:52 AM To: [email protected] Subject: RE: 13R sprinklers I am going with ignorant. In addition to this, we have to sprinkler all closets and bathrooms, install an RPZ in a hot box outside the building and they took my 42x30 drawing, shrunk it to 36x24, then rejected the plan for being less than 1/8 scale. I remember the 13/18 was the original design, but the single head calc went out about 10 years ago(?). The spec also calls for Grinnell or Star sprinklers. My guess is the engineer is just not current and not interested in being so. He probably drives and AMC Hornet and wear a leisure suit. At 10:26 AM 5/19/2010, you wrote: >This is important - LET ME PLAY DEVIL'S ADVOCATE, where is the engineer >WRONG? Quick look at Tyco LF II 4.9 pendant 12' x 12' is 13 gpm. And at 18 >gpm it's a 13.49 psi start. The sidewalls at 4.2 will do 13gpm at 9.2 psi >so you are not forced under a 7 psi start. So he won't let you use 16' x 20' >spacing? Just because one won't allow what in essence is extended coverage >doesn't make one ignorant. > >Is this not the equivalent of not allowing sched 7 and only allowing sched >40 threaded noting sched 7 has many more times the CRR? Both cases are text >book verse a real application. Perhaps some think 12' x 12' spacing is >better then EC and 40 is better than 7 when applied to a real project. How >often do we see a spec say no EC? How often do we see no reduction for QR? > >I acknowledge you did say he is reading out of the where not been listed >with special...so his argument may be flawed but his conclusion probably >isn't from his perspective. I'm sure you recall the 13/18 was the original >NFPA 13R/D spec and the first heads had no other spacing options. But it >also looks like at least in Tyco's case the low end it's the same on the >13gpm side. Yeah the dual gpm is gone. But an engineer can spec any >density greater than the minimum. > >I didn't talk with the engineer perhaps he/she/it is ignorant or perhaps >just exercising engineering prerogative like all the other times we see it. > > >Again that was the other side of the coin. I'M ON YOUR SIDE TODD. I >wouldn't cost the owner extra money in what will probably be a lot of extra >heads but I don't see anything WRONG here. > >Chris Cahill, P.E. >Fire Protection Engineer >Sentry Fire Protection, Inc. > >763-658-4483 >763-658-4921 fax > >Email: [email protected] > >Mail: P.O. Box 69 > Waverly, MN 55390 > >Location: 4439 Hwy 12 SW > Waverly, MN 55390 >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of >[email protected] >Sent: Wednesday, May 19, 2010 8:39 AM >To: [email protected] >Subject: RE: 13R sprinklers > >Todd , > Are you saying the engineer has seen and has read these sections of 13R and >still doesn't understand the requirements ? If so , you may have to go over >his head to a higher authority or say a prayer and try to appease him as >best you can. > >Good Luck , > >Lamar Vaughn , SET > > >---- Todd Williams <[email protected]> wrote: > > Discharge - 6.7.1.1.1, Coverage - 6.7.1.3.1. NFPA 13R (2002) > > > > > > > > At 08:23 AM 5/19/2010, you wrote: > > >I'd ask him to please, for your edification, cite the sections of > > >the NFPA Standard where he derived his specification data. > > > > > >I guess he was looking at sprinkler data sheets and when it didn't > > >say that the sprinkler is designed for 0.10 or whatever gpm/sq. ft > > >he thinks it falls into that category? > > > > > > > > >Craig L. Prahl, CET > > >Fire Protection Specialist > > >Mechanical Department > > >CH2MHILL > > >Lockwood Greene > > >1500 International Drive > > >Spartanburg, SC 29304-0491 > > >Direct - 864.599.4102 > > >Fax - 864.599.8439 > > >[email protected] > > >http://www.ch2m.com > > > > > >-----Original Message----- > > >From: [email protected] > > >[mailto:[email protected]] On Behalf Of Todd >Williams > > >Sent: Wednesday, May 19, 2010 6:11 AM > > >To: [email protected] > > >Subject: 13R sprinklers > > > > > >I am working on a project with a rather ignorant engineer who will > > >not accept listed flow requirements for residential sprinklers. He is > > >insisting on using the 12 x 12 spacing, 13 gpm for multiple sprinkler > > >flow and 18 for single sprinkler flow (we have to calculate both). My > > >question may be one of semantics, but this is what the engineer is > > >hanging everything on. Both the above spacing and discharge > > >requirements are under sections entitled "Sprinklers That Have Not > > >Been Listed with Specific (Discharge/Coverage) Criteria". Since > > >virtually all of the residential sprinklers I am aware of have > > >specific design and coverage criteria, am I to assume based on the > > >wording that sprinklers with specific criteria cannot be used under > > >this section? If so, are there any sprinklers without specific > > >criteria currently on the market? > > > > > >Todd G. Williams, PE > > >Fire Protection Design/Consulting > > >Stonington, CT > > >860.535.2080 > > >www.fpdc.com > > > > > >_______________________________________________ > > >Sprinklerforum mailing list > > >[email protected] > > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > >For Technical Assistance, send an email to: [email protected] > > > > > >To Unsubscribe, send an email to:[email protected] > > >(Put the word unsubscribe in the subject field) > > >_______________________________________________ > > >Sprinklerforum mailing list > > >[email protected] > > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > >For Technical Assistance, send an email to: [email protected] > > > > > >To Unsubscribe, send an email to:[email protected] > > >(Put the word unsubscribe in the subject field) > > > > Todd G. Williams, PE > > Fire Protection Design/Consulting > > Stonington, CT > > 860.535.2080 > > www.fpdc.com > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > For Technical Assistance, send an email to: [email protected] > > > > To Unsubscribe, send an email to:[email protected] > > (Put the word unsubscribe in the subject field) >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)
