There are some heads that we use that are extended coverage, but only listed 
for light hazard. They have smaller k factors (5.6 and 8) than the EC heads 
that are listed for OH (11.2 and 14), plus they are about 30-50% less per head.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Tuesday, June 08, 2010 1:08 PM
To: [email protected]
Subject: Department of Insurance

 
I'm sure this varies from state to state but here in NC it's not uncommon
for state owned buildings to include the DOI spec in the contract spec's. If
anyone's familiar with this particular version of it I have a quick
question: Ordinary Hazard group-1 is the minimum design allowed but they do
give a couple exceptions. One is that QR & QREC heads listed for light
hazard are permitted as long as OH-1 density is still achieved. What would
be the benefits of applying this exception? 

Thanks!
Brian Harris

 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to