Todd, if a drum goes up, there'd have to be a heckuva wind to not have the
sprinklers activate- even by radiant heat. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Monday, July 12, 2010 2:45 PM
To: [email protected]
Subject: RE: Flammable Liquid storage in open sheds

And since the building has no walls, how is wind going to factor in?



At 02:30 PM 7/12/2010, you wrote:
>And then there's that ever elusive, non-conforming to anything, type of 
>storage container that so often pops up.  Chemical storage is one of 
>the most aggravating things I have to deal with.  Everyone expects 
>cookie-cutter answers.  Yeah, I wish.  Then there's the chase your tail 
>in a circle Code search for containment that can confuse the daylights 
>out of people.
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of George 
>Church
>Sent: Monday, July 12, 2010 2:30 PM
>To: [email protected]
>Subject: RE: Flammable Liquid storage in open sheds
>
>and just when you think you've tracked down all the questions, you open 
>up NFPA 30 and then the phone, "relieving or non-relieving?"
>
>NFPA 30 has been given to us to add back the fun we used to have with 
>231C, which many of us don't get to experience as much with the 
>popularity of ESFRs.
>I loved asking aisle widths for a spec whse, knowing the answer.
>
>glc
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of 
>[email protected]
>Sent: Monday, July 12, 2010 2:09 PM
>To: [email protected]
>Subject: RE: Flammable Liquid storage in open sheds
>
>There are a lot of variables that need to be known before answering a 
>question like that.
>
>Depending on what building or fire code applies the answers can vary, 
>also the location of the shed with respect to exposure of other 
>buildings or public ways can factor in and in a lot of cases with a 
>Class III combustible, there may not be any need whatsoever for any 
>kind of fixed fire protection.  There needs to be some code research 
>performed and you need to know what the material is.  You can spray all 
>the water you want on certain types of combustible liquids and 
>accomplish nothing, you may need foam or foam-water.
>
>Too many unknowns here.
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of sam b
>Sent: Monday, July 12, 2010 1:56 PM
>To: [email protected]
>Subject: Flammable Liquid storage in open sheds
>
>Hii..
>
>Need some help
>
>Storage:in drums
>Flammaeble liquid: Class III
>Rack storage up to max 5 m.
>Open shed storage with no walls (max height of shed is 7 m at eave) .
>
>
>Can i know what sort of protection I need to provide(Sprinkler 
>system?). I checked NFPA 30 .but couldnt  find the exact thing.
>
>I think chapter 15,NFPA2008 edition suits the scenario. But what sort 
>of protection and design density to consider.
>
>Can anyone give me a quick answer.?
>
>Thaanks in advance
>
>Regards
>Sam
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field) 
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field) 
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to