How do you fill the systems without a JP?

----- Original Message -----
From: [email protected] 
<[email protected]>
To: [email protected] <[email protected]>
Sent: Tue Dec 07 07:22:41 2010
Subject: RE: High Rise Office Jockey pump

Yes Ron I understand that the leakage is related to UG.  That's why I'm asking 
how a JP applies to an aboveground (in the building) system.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Monday, December 06, 2010 5:53 PM
To: [email protected]
Subject: Re: High Rise Office Jockey pump

Craig,

Look in 2010 20/4.25 for perhaps a better explanation. That business
about allowable leakage applies to UG piping. There's a ".normal drops
in pressure.." clause in that sentence also and that refers to
fluctuations for any reason.

On Mon, Dec 6, 2010 at 2:22 PM,  <[email protected]> wrote:
> "NFPA 20 2007, A.5.14.4 (1) A jockey pump is USUALLY required with 
> automatically controlled pumps."
>
> So based on that statement what would be an example where a JP would USUALLY 
> not be required?
>
> "A.5.24 Pressure maintenance (jockey or make-up) pumps should be used where 
> it is desirable to maintain a uniform or relatively high pressure on the fire 
> protection system. A jockey pump should be sized to make up the allowable 
> leakage rate within 10 minutes or 1 gpm (3.8 L/min), whichever is larger."
>
> But I should have no leakage, So.......?
>
> "5.24.1 Pressure maintenance pumps shall have rated capacities not less than 
> any normal leakage rate."
>
> My leakage rate should be zero?
>
>
>
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Jack Carlson
> Sent: Monday, December 06, 2010 5:08 PM
> To: [email protected]
> Subject: RE: High Rise Office Jockey pump
>
>
> I seem to recall being told that a JP was required to keep the main pump from 
> cycling on and off due to minor pressure fluctuations.
>
>
> Jack W. Carlson, SET
> Triple "A" Fire Protection, Inc.
> Cell - 706.247.5050
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Monday, December 06, 2010 4:52 PM
> To: [email protected]
> Subject: RE: High Rise Office Jockey pump
>
> The question is what is the purpose of a JP in this application?
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: Monday, December 06, 2010 4:50 PM
> To: [email protected]
> Subject: Re: High Rise Office Jockey pump
>
> So is the question this:
>
> The building needs a fire pump to meet hose emends at the roof.
>
> or:
>
> To meet hose demand at the roof the municipal pump kicks in.
>
> On Mon, Dec 6, 2010 at 1:42 PM,  <[email protected]> wrote:
>> It's supplied off a pump supplemented private fire main.
>>
>> Craig L. Prahl, CET
>> Fire Protection
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> CH2MHILL Extension  74102
>> [email protected]
>>
>>
>>
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of Ronl.Fletcher
>> Sent: Monday, December 06, 2010 4:39 PM
>> To: [email protected]
>> Subject: RE: High Rise Office Jockey pump
>>
>> The artificially high pressure created by the jockey pump is usually 
>> necessary to prevent the main pump from starting because of fluctuations in 
>> the city pressure. If you have a very flat city curve it may be difficult to 
>> get a enough of a pressure drop from opening a hose valve to start the main 
>> pump.
>>
>> Ron Fletcher
>> Aero Automatic
>> Phoenix, AZ
>>
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of 
>> [email protected]
>> Sent: Monday, December 06, 2010 1:56 PM
>> To: [email protected]
>> Subject: RE: High Rise Office Jockey pump
>>
>> 132 psi static, 120 psi residual,  is that low pressure?
>>
>> Craig L. Prahl, CET
>> Fire Protection
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> CH2MHILL Extension  74102
>> [email protected]
>>
>>
>>
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of 
>> [email protected]
>> Sent: Monday, December 06, 2010 3:47 PM
>> To: [email protected]
>> Subject: Re: High Rise Office Jockey pump
>>
>> That is the main reason for a jockey (pressure maintenance) pump.  If the
>> fire pump were to start into a low pressure line, the differential could
>> cause physical damage to the piping and supports.
>>
>> Thank You
>>
>> Rahe Loftin, P.E.
>> Region 7 - GSA
>> Cell - 817-371-3102
>>
>>
>>
>>
>>
>>             Todd Williams
>>             <[email protected]>                                             To
>>             Sent by:                  [email protected]
>>             sprinklerforum-bo                                          cc
>>             un...@firesprinkl
>>             er.org                                                Subject
>>                                       Re: High Rise Office Jockey pump
>>
>>             12/06/2010 02:17
>>             PM
>>
>>
>>             Please respond to
>>             sprinklerfo...@fi
>>              resprinkler.org
>>
>>
>>
>>
>>
>>
>> For one, so that there is no or little surge in pressure when the
>> fire pump kicks in
>>
>>
>> At 03:06 PM 12/6/2010, you wrote:
>>>I'm not used to buildings where there's nothing in it that will
>>>leave a huge smoking crater so got a question.
>>>
>>>8 story office building, need to meet the 100 psi requirement for
>>>the top remote hose connection, engineer has spec'd an electric fire
>>>pump and jockey pump set.
>>>
>>>There is sufficient pressure and flow at the BOR for sprinkler
>>>system operation but not hose.
>>>
>>>Is there really a need for a jockey pump on this type of
>>>install?  Since JP's are typically for maintaining pressure on
>>>underground systems where leakage is typical what's the purpose in a
>>>system like this?
>>>
>>>Any NFPA verbiage which permits their omission?  So far I haven't
>>>found anything specific.
>>>
>>>Craig L. Prahl, CET
>>>Fire Protection
>>>CH2MHILL
>>>Lockwood Greene
>>>1500 International Drive
>>>Spartanburg, SC  29304-0491
>>>Direct - 864.599.4102
>>>Fax - 864.599.8439
>>>CH2MHILL Extension  74102
>>>[email protected]
>>>
>>>_______________________________________________
>>>Sprinklerforum mailing list
>>>[email protected]
>>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>>For Technical Assistance, send an email to: [email protected]
>>>
>>>To Unsubscribe, send an email to:[email protected]
>>>(Put the word unsubscribe in the subject field)
>>
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860.535.2080
>> www.fpdc.com
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
>
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to