If you're coming off a tank you're obviously running through some underground piping. So the standard setup of Fire pump/Jockey pump would be most appropriate.
Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Tuesday, December 07, 2010 9:24 AM To: [email protected] Subject: RE: High Rise Office Jockey pump - segue Let's take this one step further. If you have a fire pump taking suction from a tank that only feeds a dry system. What alternative is there to providing a dry valve and a jockey pump that pressurizes 4 ft of pipe? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)