Hi Ralph,
I am not experience, but I want to give my opinion .I think if you make the 
flow 
from PRV to be out of network (to drain e.g.).because the purpose of this valve 
is open when the pressure exceed the limited of the pump.
Please All, if I am wrong correct.
Thank you
 



________________________________
From: Ralphy Henderson <[email protected]>
To: [email protected]
Sent: Tue, December 7, 2010 7:20:35 PM
Subject: Pumps - PRV Piped Back to Source

Hello,
When NFPA #20 requires a pressure relief valve in accord with 5.18.1.1 for a 
diesel pump is it an acceptable practice to pipe the PRV discharge piping back 
to the source piping? The source is a city water main. I see NFPA 20 has some 
info on this but I've never seen it done and was wondering if this would be 
designed similar to a flow meter test loop?

Thanks,
Ralph





      