So where is the cut-off between repair and new installation? If you replace all of the existing pipe, fittings, sprinklers and hangers, etc. with exact new duplicates in an existing 30,000 building, is that a repair? If you replace some black steel pipe with galvanized, does that now become a new installation?

At 11:32 AM 1/12/2011, you wrote:
NFPA 25 does not require verification for repair work (provided you
are replacing like with like).  Verification of adequacy per
specification is a different story that may have nothing to do with
what is required by the standards.  Some reasons can be less than
honorable.

Roland


On Jan 12, 2011, at 8:14 AM, Doug Hicks wrote:

The dry pipe protects the overhang of a walkway, no attic.  the
original install is about 20 years old.  About 6 years ago, 2 more
low hazard buildings were built and the dry pipe system was
extended. The 2 new buildings are each protected by  a separate wet
system.  All the fire water comes from the original street
connection. The extension increased the protected area about 35-40
%.  I assume hydraulic Calcs were done by a licensed person. I tried
to type that with a straight face.  No increase in pipe sizes were
done.  I do not know what edition of 13 was used for any of the
sprinkler work.   I doubt that any water supply information is on
file anyplace.  So if Calcs are needed, I will have to have a
qualified person do that for me.  My local AHJ allows do whatever I
want.   So the decision will be up to the client and his engineer.

I will print this out, we have a meeting at 9:00 AM.   After the
meeting I am sure I will have more questions.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to