Permitting is the cutoff.

Here the regulations state replacement for maintenance does not require any
AHJ involvement. If you change 1 item with a different item, then we are
required to submit. If it is like for like, that is not a repair.
R/
Matt


 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of Todd Williams
> >Sent: Wednesday, January 12, 2011 10:44 AM
> >To: [email protected]
> >Subject: Re: Hydraulic Calcs
> >
> >So where is the cut-off between repair and new installation? If you
> >replace all of the existing pipe, fittings, sprinklers and hangers,
> >etc. with exact new duplicates in an existing 30,000 building, is
> >that a repair? If you replace some black steel pipe with galvanized,
> >does that now become a new installation?
> >
> >
> >At 11:32 AM 1/12/2011, you wrote:
> >>NFPA 25 does not require verification for repair work (provided you
> >>are replacing like with like).  Verification of adequacy per
> >>specification is a different story that may have nothing to do with
> >>what is required by the standards.  Some reasons can be less than
> >>honorable.
> >>
> >>Roland
> >>
> >>
> >>On Jan 12, 2011, at 8:14 AM, Doug Hicks wrote:
> >>
> >>>The dry pipe protects the overhang of a walkway, no attic.  the
> >>>original install is about 20 years old.  About 6 years ago, 2 more
> >>>low hazard buildings were built and the dry pipe system was
> >>>extended. The 2 new buildings are each protected by  a separate wet
> >>>system.  All the fire water comes from the original street
> >>>connection. The extension increased the protected area about 35-40
> >>>%.  I assume hydraulic Calcs were done by a licensed person. I tried
> >>>to type that with a straight face.  No increase in pipe sizes were
> >>>done.  I do not know what edition of 13 was used for any of the
> >>>sprinkler work.   I doubt that any water supply information is on
> >>>file anyplace.  So if Calcs are needed, I will have to have a
> >>>qualified person do that for me.  My local AHJ allows do whatever I
> >>>want.   So the decision will be up to the client and his engineer.
> >>>
> >>>I will print this out, we have a meeting at 9:00 AM.   After the
> >>>meeting I am sure I will have more questions.
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>[email protected]
> >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >>For Technical Assistance, send an email to: [email protected]
> >>
> >>To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >>(Put the word unsubscribe in the subject field)
> >
> >Todd G. Williams, PE
> >Fire Protection Design/Consulting
> >Stonington, CT
> >860.535.2080
> >www.fpdc.com
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >No virus found in this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.872 / Virus Database: 271.1.1/3374 - Release Date: 01/12/11
> >01:38:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to