We run into this issue more with fire alarm systems.  Given the evolution of 
fire alarm systems over the years there is no way we would approve a like for 
like replacement of some of these POS fire alarm systems that used to be 
allowed.

Rich Richardson
Seattle Fire Department

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Wednesday, January 12, 2011 11:51
To: [email protected]
Subject: Re: Hydraulic Calcs

That would be a change of occupancy and so require a new analysis.
Different issue. Nothing changes, only replacing the system exactly as
it was and it's a repair unless someone like Rich (AHJ) wants to call
it otherwise

On Wed, Jan 12, 2011 at 11:31 AM, Todd Williams <[email protected]> wrote:
> If a system is installed that is an exact duplicate of an existing system,
> which it is to replace, is that considered a new system under the Code or a
> "repair" of a system under 25? Where is the cut-off between the two? How
> would any of the AHJ's out there address this?
>
> Now George, supposed your building has 12ft storage of expanded plastics or
> flammable liquid storage? Most likely the pipe schedule system is not going
> to be able to protect those occupancies. Would you swap the system old for
> new as it was installed? How would the attorney for the plaintiff react to
> that?
>
> I didn't even bring up the issues about 3/4", 3-1/2" and 5" pipe.
>
>
>
> At 12:33 PM 1/12/2011, you wrote:
>>
>> So you run new UG into a building that was legally pipe schedule because
>> the calc (that wasn't required under the valid but old design criteria)
>> doesn't work? It doesn't have to, its designed to the applicable code at
>> installation.
>>
>> George Church'
>> Rowe Sprinkler
>> [email protected]
>> 570-837-7647
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Todd Williams
>> Sent: Wednesday, January 12, 2011 12:20 PM
>> To: [email protected]
>> Subject: Re: Hydraulic Calcs
>>
>> Ok, so in Doug's situation, it constitutes a new installation and not
>> repair work (based on your first statement) and it is based on a prior
>> design. However, as a new installation wouldn't the design need to meet
>> current Codes irregardless of when the design was done and probably require
>> hydraulic calculations?
>>
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to