We are mixing apples and oranges. The below focused on protecting the building while avoiding excessive loss of records. Recent tests that led to changes in 13 identified that even presenting a heavier fuel load, a light hazard classification was acceptable because it took so long to generate enough heat to activate the sprinkler (50 minutes or so was a common outcome). This does not minimize loss of records but provides adequate protection for the building.

Roland

On Jan 20, 2011, at 12:18 PM, Jim Davidson wrote:

Rolling Aisle File Storage presents a severe fire load for the sprinkler system to suppress. There were studies conducted by:

1. Fire Protection Study, Mobile Compact Shelving Fire Tests, “Archives II”, Gage-Babcock & Associates, Dated June 1990.

2. Full Scale Fire Tests of Sprinklered Mobile Shelving Units for National Library of Canada, Gage-Babcock & Associates, Dated May 1992.

3. Full-Scale Fire Tests and the Development of Design Criteria for Sprinkler Protection of Mobile Shelving Units, G.D. Lougheed, J.R. Mawhinney, and J. O’Neill, Fire Technology, First Quarter 1994, Volume 30, Number 1, pp.’s. 98 - 133.


Fire testing involving archival records stored in mobile compact shelving indicated that sprinklers were not able to prevent extensive damage to records. An analysis of those fire tests indicated that standard 212F temperature rated sprinklers did not operate until the fire was well underway, particularly in the lower levels of the units. Once the sprinklers operated, the water spray could not effectively reach and control the fire. The close proximity of the rows of stack units combined with typical unit depth prevented the water discharge from the overhead sprinklers from wetting the records and containers stored in the units, and to effectively control and extinguish the fire.

Additional fire testing for the General Services Administration (GSA) entitled “Archives II” has verified that quick-response (QR) sprinklers along with enhancements in the operation and construction features in the stack units greatly limited the fire damage to archival records as compared to previous methods of fire protection. The concept included a modification of the controls for electric motor-driven unit, whereby in the early stages of a fire following activation of a smoke detector, the rows automatically shift to a uniform 4 to 5 inches spacing between each adjacent row in a stack area. The verification fire tests indicated that with QR sprinklers effective fire control was achieved with damage primarily limited to two rows exposed to the incipient fire.

The first concept is not necessarily limited to electric motor- driven stack systems. This concept can be applied to mechanical assist systems when based on having at all times a minimum 6-inch space between the mechanical shelving units. This will necessitate the removal of one, or more as required, moving shelf storage unit on each side of the fixed center shelf unit and the installation of a “bumper” to maintain a minimum 6-inch space between the shelving units at all times.

It was clear from the results of Archives II, Test No. 2 that close proximity of the adjacent rows of stacks presented the same problems for effective fire control as in the Factory Mutual (FM) tests conducted on 1978 on Rolling Aisle Storage Arrangements. The benefit of the QR sprinkler over the standard sprinklers was evident in that the fire did not “jump” or spread across the access aisle before or after sprinkler activation. In the previous FM tests, the fire spread across the access aisle before the first standard sprinkler actuated.

Since the sprinkler spray did not reach the fire burning below in the lower levels of the stack units, simply increasing the water flow rate from the sprinklers would not likely result in better extinguishment.

The sprinkler system used in the Archives II test was designed to provide a water flow rate of 30 gpm/sprinkler. This resulted in an average system design density of 0.30 gpm/ft2. It is important to recognize that use of the Archives II recommendations necessitates verification that the existing sprinkler system can deliver the design densities used in the tests of vertical stacks.

The hydraulic calculations should be based on a design density of 0.30 gpm over the hydraulically remote 3,000-sq. ft. using QR sprinkler heads.

In addition to the sprinkler system modifications the storage shelving arrangement will need to be modified as follows:

1. One or more of the rolling shelving unit(s) will need to be removed on either side of the center non-moveable shelving section. This applies to all of the shelving units arrays. 2. Provide a mechanical means to maintain at all times a minimum 6- inch space between each shelving unit. 3. The compartment containing the rolling aisle storage shall be cut off from the remainder of the facility with two hour fire rated barrier (ceiling, floor and walls), with openings protected by 1½ hour, Class B, fire rated protective devices..

This is not just a sprinkler contractor solution.

Hope this helps.

Have a fire safe day!

Jim Davidson

Davidson Associates
Fire Protection • Medical Gas • Code Consulting
302-994-9500   Fax:302-234-1781


-----Original Message-----
From: [email protected] [mailto:[email protected] ] On Behalf Of Matthew J. Willis
Sent: Thursday, January 20, 2011 2:46 PM
To: [email protected]
Subject: RE: Rolling medical file storage

I am surprised it is not a deluge....

If they were put in since last inspection, Yes code violation. (4.1.6)

If built that way, No. (1.1.2)



R/
Matt





Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

-----Original Message-----
From: [email protected] [mailto:sprinklerforum-
[email protected]] On Behalf Of Gregg Key
Sent: Thursday, January 20, 2011 1:27 PM
To: [email protected]
Subject: Rolling medical file storage

It has been a while since I have been on and I think this has been
discussed
before but cant find it in the archives so here I go.

Doing a NFPA 25 inspection and find a medical storage room with rolling files that are within 8" of the sprinklers. Sprinklers spaced 12x12. This system has 8 rolling files and only room for 1 to be open at a time so no way to get adequate coverage. Was told it was installed like this from beginning and was accepted. What sayest the Sprinkler forumites? code
violation or not? How would you address it? BTW this is at a State
facility.
Thanks

C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.872 / Virus Database: 271.1.1/3375 - Release Date: 01/19/11
13:34:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to