We are just finishing a court case where the total flooding system was not 
designed to take into account "soak" time and room leakage over the required 
soak time. Total loss and deformation of structural steel beams. 

The industry can recover wet paper by freeze drying, but not burnt paper. 
Depends on the clients ability to handle the expected loss. The Temple Law 
library fire many years ago showed what can happen if there is no sprinkler 
protection, the library had a fire where some of the most historic law 
documents were stored and because of aversion to water damage sprinklers were 
not provided in the vault where the collection was stored, the area outside the 
vault had sprinkler protection. When the fire was extinguished the collection 
in the vault was almost all consumed while the collections outside the vault 
had a 90% restoration rate because they were wet.

Depends on which direction the Owner wants to go.

Automatic fire sprinkler protection is usually the best way to protect 
contents, occupants, structure and fire fighters because there are simple and 
reliable.

Have a fire safe day.
    

Jim Davidson 
 
Davidson Associates 
Fire Protection • Medical Gas • Code Consulting  
302-994-9500   Fax:302-234-1781



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Thom
Sent: Thursday, January 20, 2011 6:30 PM
To: [email protected]
Subject: RE: Rolling medical file storage

Jim:

Based upon you "Risk Aversion" Less water not more would seem to be the answer. 
So much so that No water would save the building and those un replaceable 
"Paper files"

Total flooding gas system?????

Water damage can be just a damaging to paper as fire. Your own what if, should 
support the owner spending the $$$ for gas.



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim Davidson
Sent: Thursday, January 20, 2011 3:45 PM
To: [email protected]
Subject: RE: Rolling medical file storage

Roland,

It is usually considered as an Ord Group II or Extra hazard area within a light 
hazard occupancy. This type of storage should be protected based on the fuel 
load present not the general hazard class of the facility. 

You need to remember that when this type of file storage burns someone is going 
to pay for the loss of the files and the resulting loss of income for the 
institution. And the contractor referring to NFPA 13 with the referenced 
testing done by the GSA available and not refuted by NFPA 13 could leave the 
sprinkler contractor hanging, especially if the contractor does not look at the 
details of the shelving units being used, and the configuration of the storage 
modules.

Regards

   

Jim Davidson 
 
Davidson Associates 
Fire Protection • Medical Gas • Code Consulting  
302-994-9500   Fax:302-234-1781

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to