Roland,

Yes we had to provide a 6 inch separation between the shelf units, in the GSA 
testing there was one series of testing with solid vertical barriers, the test 
data did indicate that the solid vertical barriers did slow the fire down and 
prevented the fire from running the shielded shelf levels. However, I agree 
that the 250 sq ft units are different from what my clients were using. 

I am just trying to prevent the contractor from becoming a participant in the 
loss settlement.  

Have a fire safe day!

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Thursday, January 20, 2011 7:16 PM
To: [email protected]
Subject: Re: Rolling medical file storage

I wasn't referring to the general classification of the building but  
to the Compact Storage itself being light hazard (as per 20.6.1) -  
again that is limited to 250 sf.  As such, still sounds to me like we  
are talking about apples and oranges.

For your arrangement I agree with you but would suggest the interior  
metal barriers play a bigger role than the higher density (though not  
saying light hazard) due to the slow activation of sprinklers typical  
produced by metal enclosed records.  Does this situation have the  
automatic separation creating that small gap identified in the early  
studies?

It doesn't sound like a modified 20.7 with a reduced height, thus the  
protection should be defined by the EOR (by their appropriate subs)  
verses a big X with sprinkler per 13 and leaving it up to the  
contractor.

Roland



On Jan 20, 2011, at 2:44 PM, Jim Davidson wrote:

> Roland,
>
> Most of the rolling aisle file storage areas that I have reviewed  
> are approximately 8,000 sq. ft. in area, usually on the first floor  
> on in a basement area. The racks are approximately 8 ft tall and  
> approximately 20 to 30 ft in length without solid steel transverse  
> barriers. This type of storage is not considered as a "light hazard"  
> occupancy based on fuel load. It is usually considered as an Ord  
> Group II or Extra hazard area within a light hazard occupancy. This  
> type of storage should be protected based on the fuel load present  
> not the general hazard class of the facility.
>
> You need to remember that when this type of file storage burns  
> someone is going to pay for the loss of the files and the resulting  
> loss of income for the institution. And the contractor referring to  
> NFPA 13 with the referenced testing done by the GSA available and  
> not refuted by NFPA 13 could leave the sprinkler contractor hanging,  
> especially if the contractor does not look at the details of the  
> shelving units being used, and the configuration of the storage  
> modules.
>
> Regards
>
>
>
> Jim Davidson

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to