Yeah but where does it state that? NFPA #13R doesn't require sprinklers in
bathrooms under 55 sq. ft. Ch 6.9 (2007 ed) when talking about bathrooms,
doesn't say "within dwelling units" as it does with 6.9.3 for the sprinkling of
closets, pantries etc.
The distinction, as far as I can tell, of"within" and "outside" the dwelling
units only applies to design criteria and not location - otherwise concealed
combustible spaces outside the dwelling unit would have to sprinkled which is
obviously not the case.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)