Sorry, not so...please provide documentation showing where that's stated. Whenever you use 13R you use the standard throughout the building except where specifically indicated by 13R. The only time 13R refers you back to NFPA 13 for areas outside the dwelling unit is primarily for discharge densities, spacing, etc and NOT sprinkler locations
You'll notice in the following appendix material for 6.8.2 that sprinkler LOCATION is not mentioned - deliberately. A.6.8.2 It is only the intent of NFPA 13R to reference the sprinkler discharge (flow and pressure), number of design sprinklers, and position of sprinklers (distance from walls, ceilings, and other sprinklers) requirements of NFPA 13, Standard for the Installation of Sprinkler Systems. Other rules from NFPA 13 such as sprinklering of combustible concealed spaces, hose stream demand, and water supply duration are not intended to be referenced by 6.8.2. --- On Fri, 2/11/11, G. Tim Stone <[email protected]> wrote: From: G. Tim Stone <[email protected]> Subject: Re: Friday Brainfreeze - 13R Outside the dwelling Units Bathrooms To: "[email protected]" <[email protected]> Date: Friday, February 11, 2011, 9:14 PM If you are outside the dwelling unit, it reverts back to NFPA 13. Chapter 8. Sent from my iPhone G Tim Stone On Feb 11, 2011, at 3:01 PM, Ralphy Henderson <[email protected]> wrote: > Yeah but where does it state that? NFPA #13R doesn't require sprinklers in > bathrooms under 55 sq. ft. Ch 6.9 (2007 ed) when talking about bathrooms, > doesn't say "within dwelling units" as it does with 6.9.3 for the sprinkling > of closets, pantries etc. > > The distinction, as far as I can tell, of"within" and "outside" the dwelling > units only applies to design criteria and not location - otherwise concealed > combustible spaces outside the dwelling unit would have to sprinkled which is > obviously not the case. > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)