How can a bathroom be outside the dwelling unit? That's like saying
living rooms outside the dwelling area.

On Fri, Feb 11, 2011 at 2:08 PM, Ralphy Henderson
<[email protected]> wrote:
> Sorry, not so...please provide documentation showing where that's stated. 
> Whenever you use 13R you use the standard throughout the building except 
> where specifically indicated by 13R. The only time 13R refers you back to 
> NFPA 13 for areas outside the dwelling unit is primarily for discharge 
> densities, spacing, etc and NOT sprinkler locations
>
> You'll notice in the following appendix material for 6.8.2 that sprinkler 
> LOCATION is not mentioned - deliberately.
>
> A.6.8.2  It is only the intent of NFPA 13R to reference the sprinkler 
> discharge (flow and pressure), number of design sprinklers, and position of 
> sprinklers (distance from walls, ceilings, and other sprinklers) requirements 
> of NFPA 13, Standard for the Installation of Sprinkler Systems. Other rules 
> from NFPA 13 such as sprinklering of combustible concealed spaces, hose 
> stream demand, and water supply duration are not intended to be referenced by 
> 6.8.2.
>
> --- On Fri, 2/11/11, G. Tim Stone <[email protected]> wrote:
>
> From: G. Tim Stone <[email protected]>
> Subject: Re: Friday Brainfreeze - 13R Outside the dwelling Units Bathrooms
> To: "[email protected]" <[email protected]>
> Date: Friday, February 11, 2011, 9:14 PM
>
> If you are outside the dwelling unit, it reverts back to NFPA 13. Chapter 8.
>
> Sent from my iPhone
> G Tim Stone
>
>
> On Feb 11, 2011, at 3:01 PM, Ralphy Henderson <[email protected]> 
> wrote:
>
>> Yeah but where does it state that? NFPA #13R doesn't require sprinklers in 
>> bathrooms under 55 sq. ft. Ch 6.9 (2007 ed) when talking about bathrooms, 
>> doesn't say "within dwelling units" as it does with 6.9.3 for the sprinkling 
>> of closets, pantries etc.
>>
>> The distinction, as far as I can tell, of"within" and "outside" the dwelling 
>> units only applies to design criteria and not location - otherwise concealed 
>> combustible spaces outside the dwelling unit would have to sprinkled which 
>> is obviously not the case.
>>
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to