Cory, the 13 handbook explains it a little better, saying it is because storage can be put under the lowest landing and thus the requirement for a sprinkler at top as well as under the lowest landing, exhibit 8.29 of the handbook shows where the head is required.
Richard Carr, SET Design Manager Associated Sprinkler Co., LLC 336.373.3901 ext 217 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Friday, March 11, 2011 7:41 AM To: [email protected] Subject: RE: Sprinkler under first accessible landing Cory, When I hear "first accessible landing" I picture the landing directly above the lowest exit door way. I do not think it has anything to do with a access panel. I put the sprinklers in the ceiling at the top of the shaft and under the first accessible landing. Dewayne Martinez Design Build Fire Protection New Berlin, WI -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Cory Power Sent: Friday, March 11, 2011 6:19 AM To: [email protected] Subject: Sprinkler under first accessible landing I have an an engineer asking to provide a sprinkler under the first landing of a non-combustible stairwell. The spec for the job states that "Sprinkler shall be installed at top of shaft. Space below first landing is considered concealed, non-accessible, non-combustible, and hence does not require sprinkler protection." he engineer who is reviewing my plans sent me an email stating the following: *8.15.3.2 Noncombustible Construction.* *8.15.3.2.1 *In noncombustible stair shafts having noncombustible stairs with noncombustible or limited-combustible finishes, sprinklers shall be installed at the top of the shaft and under the first accessible*landing*above the bottom of the shaft. We always took this to mean the sprinklers are required under the first landing? And by accessible we took this to mean access could be provided by a access panel.." Is this the way I should be interpreting the code? Do I still have to sprinkler under the landing and make sure there's an access hatch? or should I be able to omit it like the spec indicates? I have been following this forum for a while now. This is the first question I have posted. - Cory _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) This email and any attached files are confidential and intended solely for the intended recipient(s). If you are not the named recipient you should not read, distribute, copy or alter this email. Any views or opinions expressed in this email are those of the author and do not represent those of the company. Warning: Although precautions have been taken to make sure no viruses are present in this email, the company cannot accept responsibility for any loss or damage that arise from the use of this email or attachments. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)