We don't bash anyone PE or non-PE who has interest in this forum for the sake 
of learning.  It's those who think they know it all and have no desire to learn 
or listen that we like to barbeque.  ;)

Active participation that has educational value is always welcome and 
encouraged.

Stuff showing how dumb or arrogant some people are also provides entertainment 
value which we need now and then as well.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Law, Kevin W
Sent: Friday, March 11, 2011 10:55 AM
To: [email protected]
Subject: RE: Sprinkler under first accessible landing

Be gentle, now.........I appreciate that you said only "no gold star" instead 
of going off on a rant about incopitent engineers.  Some of us do try to learn 
and willing to listen to reason........ 


Kevin Law, PE
Sr. Fire Protection Engineer
HVAC/Fire Protection, M&PE
Bechtel National - WTP Project 
Ph.   509-371-3280
Cell   509-531-5715

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, March 11, 2011 5:39 AM
To: [email protected]
Subject: RE: Sprinkler under first accessible landing

Under the lowest landing due to the possibility of that space being used for 
storage.  If the space is totally enclosed then there is no access for storage 
and no head is required if the stair is non-combustible.  The spec is correct.  
<sigh> The Engineer has taken some license on his quote of the 13 section.  The 
word "accessible" is not in the script.  So no gold star for him.  


NFPA 13, 2007 - 8.15.3.2.1 "In noncombustible stair shafts having 
noncombustible stairs with noncombustible or limited combustible finishes, 
sprinklers shall be installed at the top of the shaft and under the first 
landing above the bottom of the shaft."

Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cory Power
Sent: Friday, March 11, 2011 7:19 AM
To: [email protected]
Subject: Sprinkler under first accessible landing

I have an an engineer asking to provide a sprinkler under the first 
landing of a non-combustible stairwell. The spec for the job states that 
"Sprinkler shall be installed at top of shaft. Space below first landing 
is considered concealed, non-accessible, non-combustible, and hence does 
not require sprinkler protection."

he engineer who is reviewing my plans sent me an email stating the 
following:

*8.15.3.2 Noncombustible Construction.*

*8.15.3.2.1 *In noncombustible stair shafts having noncombustible stairs 
with noncombustible or limited-combustible finishes, sprinklers shall be 
installed at the top of the shaft and under the first 
accessible*landing*above the bottom of the shaft.

We always took this to mean the sprinklers are required under the first 
landing? And by accessible we took this to mean access could be provided 
by a access panel.."

Is this the way I should be interpreting the code? Do I still have to 
sprinkler under the landing and make sure there's an access hatch? or 
should I be able to omit it like the spec indicates?

I have been following this forum for a while now. This is the first 
question I have posted.


- Cory
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to