Under the lowest landing due to the possibility of that space being used for 
storage.  If the space is totally enclosed then there is no access for storage 
and no head is required if the stair is non-combustible.  The spec is correct.  
<sigh> The Engineer has taken some license on his quote of the 13 section.  The 
word "accessible" is not in the script.  So no gold star for him.  


NFPA 13, 2007 - 8.15.3.2.1 "In noncombustible stair shafts having 
noncombustible stairs with noncombustible or limited combustible finishes, 
sprinklers shall be installed at the top of the shaft and under the first 
landing above the bottom of the shaft."

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cory Power
Sent: Friday, March 11, 2011 7:19 AM
To: [email protected]
Subject: Sprinkler under first accessible landing

I have an an engineer asking to provide a sprinkler under the first 
landing of a non-combustible stairwell. The spec for the job states that 
"Sprinkler shall be installed at top of shaft. Space below first landing 
is considered concealed, non-accessible, non-combustible, and hence does 
not require sprinkler protection."

he engineer who is reviewing my plans sent me an email stating the 
following:

*8.15.3.2 Noncombustible Construction.*

*8.15.3.2.1 *In noncombustible stair shafts having noncombustible stairs 
with noncombustible or limited-combustible finishes, sprinklers shall be 
installed at the top of the shaft and under the first 
accessible*landing*above the bottom of the shaft.

We always took this to mean the sprinklers are required under the first 
landing? And by accessible we took this to mean access could be provided 
by a access panel.."

Is this the way I should be interpreting the code? Do I still have to 
sprinkler under the landing and make sure there's an access hatch? or 
should I be able to omit it like the spec indicates?

I have been following this forum for a while now. This is the first 
question I have posted.


- Cory
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to