Hard to believe sarcasm awards are scarce up in your display cabinet......
Don't quit your day job, I guess.

glc



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of steve
Sent: Monday, March 14, 2011 12:12 AM
To: AFSA
Subject: Re: Sprinkler under first accessible landing

That was me; send all kudos to my office address please.  Collections lagging 
badly.


Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: Ron Greenman <[email protected]>
Sender: [email protected]
Date: Sun, 13 Mar 2011 19:39:50
To: <[email protected]>
Reply-To: [email protected]
Subject: Re: Sprinkler under first accessible landing

Craig,

I thought it was you making fun of the architect by pointing out his 
misinterpretation was as silly as defining accessibility in this case as being 
the ADA one. I know someone mentioned it. I apologize for the attribution but 
it was praise for the satirical observation. So whoever it was: Kudos.

On Sun, Mar 13, 2011 at 6:52 PM,  <[email protected]> wrote:
> I didn't mention anything related to ADA and it's referencve to 
> "accessibility".  A stair landing has nothing to do with ADA, that would be 
> totally stupid.
>
> Hans,  sorry but if the PE read the handbook which gives an explanation he 
> would have understood the reason for the head under the FIRST landing, not 
> just ANY landing that you can access.  The two common places where storage 
> occurs are under the FIRST landing on ground level and on the extra width 
> that isn't used at the TOP of the stairs.  Some of this stuff is just too 
> simple but some who live to revel in the excellance of their superior 
> education like to make it more difficult.  So my Star detraction still 
> stands.  Sorry, just can't excuse blantant ignorance.
>
>
> Craig Prahl
> CH2MHILL/SPB
> 864-599-4102
>________________________________________
> From: [email protected] 
>[[email protected]] On Behalf Of Ron Greenman 
>[[email protected]]
> Sent: Sunday, March 13, 2011 12:28 PM
> To: [email protected]
> Subject: Re: Sprinkler under first accessible landing
>
> Problem is that the term is not defined per 13 and so do you use 
> Webster, IBC or ADA? Although a non-building person would probably 
> default to a Websteristic definition and just ask, "Can you get into 
> and use the space for something?" but a building guy will more likely 
> fall into accessible/non-accessible concealed space (which isn't even 
> in 13 in those words), or accessible through an access panel, or, per 
> Craig's comment/joke, do you use ADA and build a ramp to above the 
> ATC. Considering some of the costly insanity associated with ADA 
> interpretation there may be more truth to what Craig said than he was 
> thinking when he said it. Take Texas with horn/strobes in closets in 
> case a  deaf person is in the closet. What if it's a blind and deaf 
> person? Or in my own case. My classrooms are in the semi basement 
> (side of hill, full-flight of stairs to floor above for one egress and 
> half-flight up on the downslope side. There's also a non-compliant 
> ramp that's too steep for ADA. I also have two sinks with soap and 
> towel dispensers. One day maintenance shows up and announces that per 
> ADA they have to lower all the dispensers to some ADA height standard 
> for wheelchair accessibility. Now the sinks stay the same but the 
> towels and soap dispensers are essentially on the floor. Although I 
> could potentially have a wheelchair bound student I never have (or 
> maybe I have but he died on the ramp on his first day when he lost 
> control of his chair), but I have had numerous re-trains that have 
> hurt their backs and have trouble or even pain bending over. These 
> devices WERE non-accessible to them. Were comes into the equation 
> since I have tools and I'm not afraid to use them.
>
> On Sun, Mar 13, 2011 at 8:44 AM, Frans Stoop <[email protected]> wrote:
>> Craig,
>>
>> Don't be to greedy with the gold stars to that poor engineer or one 
>> day you might have to hand over one of your own.
>> The engineer did not take any license, he only quoted the most recent 
>> edition of NFPA 13.
>> The word "accessible" might not be in the 2007 edition, but it does 
>> show up in the 2010 edition:
>>
>> "8.15.3.2.1 In noncombustible stair shafts having noncombustible 
>> stairs with noncombustible or limited-combustible finishes, 
>> sprinklers shall be installed at the top of the shaft and under the 
>> first accessible landing above the bottom of the shaft."
>>
>> In fact the word "accessible" is the only difference in the wording 
>> of this paragraph between the two editions.
>>
>> Met vriendelijke groet / Yours sincerely,
>>
>> Frans Stoop
>> TOS architecture & fire protection
>> Netherlands <[email protected]>
>> Tel. +31-24-324 0112
>>
>>
>> At 06:39 11-3-2011 -0700, you wrote:
>>>
>>> Under the lowest landing due to the possibility of that space being 
>>> used for storage.  If the space is totally enclosed then there is no 
>>> access for storage and no head is required if the stair is 
>>> non-combustible.  The spec is correct.  <sigh> The Engineer has 
>>> taken some license on his quote of the
>>> 13 section.  The word "accessible" is not in the script.  So no gold 
>>> star for him.
>>>
>>> NFPA 13, 2007 - 8.15.3.2.1 "In noncombustible stair shafts having 
>>> noncombustible stairs with noncombustible or limited combustible 
>>> finishes, sprinklers shall be installed at the top of the shaft and 
>>> under the first landing above the bottom of the shaft."
>>>
>>> Craig L. Prahl, CET
>>> Fire Protection
>>> CH2MHILL
>>> Lockwood Greene
>>> 1500 International Drive
>>> Spartanburg, SC  29304-0491
>>> Direct - 864.599.4102
>>> Fax - 864.599.8439
>>> CH2MHILL Extension  74102
>>> [email protected]
>>>
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Cory 
>>> Power
>>> Sent: Friday, March 11, 2011 7:19 AM
>>> To: [email protected]
>>> Subject: Sprinkler under first accessible landing
>>>
>>> I have an an engineer asking to provide a sprinkler under the first 
>>> landing of a non-combustible stairwell. The spec for the job states 
>>> that "Sprinkler shall be installed at top of shaft. Space below 
>>> first landing is considered concealed, non-accessible, 
>>> non-combustible, and hence does not require sprinkler protection."
>>>
>>> he engineer who is reviewing my plans sent me an email stating the
>>> following:
>>>
>>> *8.15.3.2 Noncombustible Construction.*
>>>
>>> *8.15.3.2.1 *In noncombustible stair shafts having noncombustible 
>>> stairs with noncombustible or limited-combustible finishes, 
>>> sprinklers shall be installed at the top of the shaft and under the 
>>> first accessible*landing*above the bottom of the shaft.
>>>
>>> We always took this to mean the sprinklers are required under the 
>>> first landing? And by accessible we took this to mean access could 
>>> be provided by a access panel.."
>>>
>>> Is this the way I should be interpreting the code? Do I still have 
>>> to sprinkler under the landing and make sure there's an access 
>>> hatch? or should I be able to omit it like the spec indicates?
>>>
>>> I have been following this forum for a while now. This is the first 
>>> question I have posted.
>>>
>>> - Cory
>>
>>_______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email 
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
> They are happy men whose natures sort with their vocations. -Francis  
>Bacon, essayist, philosopher, and statesman (1561-1626) 
>_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
>to:[email protected]
> (Put the word unsubscribe in the subject field) 
>_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to