Indeed no gold star. I've had too mangy AHJs as well as engineers
selectively quote parts of codes and leave out exceptions they didn't
like, change a single word that changes the entire meaning (this is
common in NICET questions where the exact wording in the code is the
only correct answer among many that essentially say the same thing but
are incorrect), or reference a piece of code that seems to apply but
doesn't (the internal galvanizing requirement thread from the
beginning of the week?). For this issue though there is the
consideration of the accumulation of debris under the first landing
but in the case where the space is enclosed, regardless of
accessibility,this is also not an issue.

On Fri, Mar 11, 2011 at 5:39 AM,  <[email protected]> wrote:
> Under the lowest landing due to the possibility of that space being used for 
> storage.  If the space is totally enclosed then there is no access for 
> storage and no head is required if the stair is non-combustible.  The spec is 
> correct.  <sigh> The Engineer has taken some license on his quote of the 13 
> section.  The word "accessible" is not in the script.  So no gold star for 
> him.
>
>
> NFPA 13, 2007 - 8.15.3.2.1 "In noncombustible stair shafts having 
> noncombustible stairs with noncombustible or limited combustible finishes, 
> sprinklers shall be installed at the top of the shaft and under the first 
> landing above the bottom of the shaft."
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Cory Power
> Sent: Friday, March 11, 2011 7:19 AM
> To: [email protected]
> Subject: Sprinkler under first accessible landing
>
> I have an an engineer asking to provide a sprinkler under the first
> landing of a non-combustible stairwell. The spec for the job states that
> "Sprinkler shall be installed at top of shaft. Space below first landing
> is considered concealed, non-accessible, non-combustible, and hence does
> not require sprinkler protection."
>
> he engineer who is reviewing my plans sent me an email stating the
> following:
>
> *8.15.3.2 Noncombustible Construction.*
>
> *8.15.3.2.1 *In noncombustible stair shafts having noncombustible stairs
> with noncombustible or limited-combustible finishes, sprinklers shall be
> installed at the top of the shaft and under the first
> accessible*landing*above the bottom of the shaft.
>
> We always took this to mean the sprinklers are required under the first
> landing? And by accessible we took this to mean access could be provided
> by a access panel.."
>
> Is this the way I should be interpreting the code? Do I still have to
> sprinkler under the landing and make sure there's an access hatch? or
> should I be able to omit it like the spec indicates?
>
> I have been following this forum for a while now. This is the first
> question I have posted.
>
>
> - Cory
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to