If you have a full complement of sprinklers above the clouds, then the cloud 
sprinklers are no different (hydraulically) than a ceiling complement below an 
interstitial space, or sprinklers below obstructions such as ducts.  NFPA 13 is 
clear on the intent the only the most demanding complement is required to be 
calculated.

My opinion only,
Steve Leyton


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Thom
Sent: Monday, March 28, 2011 2:52 PM
To: [email protected]
Subject: RE: Cloud Calculations

I would say yes to adding the two heads to the calc.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob Knight
Sent: Monday, March 28, 2011 3:48 PM
To: [email protected]
Subject: Cloud Calculations

What would the consensus be (ok, ok, I know this is the forum, but...) in an
open office enviro with uprights at the ceiling and pendent's in the ceiling
clouds in regards to calc's?  I will have a 1500 sf area w/ no reduction.  I
will obviously be calc'ing all the uprights w/in the design area, but what
about the pendent's in the clouds?  Do I calc all the ceiling cloud heads
w/in the DA?  Two heads?  

Thanks,

Bob Knight
(208) 639-8790  Direct Phone
(208) 639-8791  Direct Fax
(208) 994-1439  Cell



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to