Bad answer Todd, baaaaad answer!  But I think I'm going to go with it.  It 
means up'ing the branch lines 1 size and throwing in a grid for the area 
affected.  Neither of which is really a big deal, this time.

Bob

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Monday, March 28, 2011 4:03 PM
To: [email protected]
Subject: Re: Cloud Calculations

The problem is that no one knows how sprinklers in a room with ceiling clouds 
are going to react. I almost always calculate the full compliment for that 
reason. FM Global requires all to be calculated. I did an FMG job last year, 
2500 sqft design area with clouds; 50 sprinklers in the calc area. Overkill, 
probably. 

We really won't know what the right answer is until we get some fire testing.


At 05:47 PM 3/28/2011, you wrote:
>What would the consensus be (ok, ok, I know this is the forum, but...) in an 
>open office enviro with uprights at the ceiling and pendent's in the ceiling 
>clouds in regards to calc's?  I will have a 1500 sf area w/ no reduction.  I 
>will obviously be calc'ing all the uprights w/in the design area, but what 
>about the pendent's in the clouds?  Do I calc all the ceiling cloud heads w/in 
>the DA?  Two heads?  
>
>Thanks,
>
>Bob Knight
>(208) 639-8790  Direct Phone
>(208) 639-8791  Direct Fax
>(208) 994-1439  Cell
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to