Steve, I thought that as well, but in all my musings I also figured that the sprinklers at the cloud level were more likely to operate than say a sprinkler under a duct. I also figured in my little head that sprinklers would activate at the ceiling level as well. I understand what your point is, but how do I substantiate that with code to the inquisitive AHJ? The same would be for Thom's suggestion of two.
Bob -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Monday, March 28, 2011 3:54 PM To: [email protected] Subject: RE: Cloud Calculations If you have a full complement of sprinklers above the clouds, then the cloud sprinklers are no different (hydraulically) than a ceiling complement below an interstitial space, or sprinklers below obstructions such as ducts. NFPA 13 is clear on the intent the only the most demanding complement is required to be calculated. My opinion only, Steve Leyton -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Thom Sent: Monday, March 28, 2011 2:52 PM To: [email protected] Subject: RE: Cloud Calculations I would say yes to adding the two heads to the calc. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bob Knight Sent: Monday, March 28, 2011 3:48 PM To: [email protected] Subject: Cloud Calculations What would the consensus be (ok, ok, I know this is the forum, but...) in an open office enviro with uprights at the ceiling and pendent's in the ceiling clouds in regards to calc's? I will have a 1500 sf area w/ no reduction. I will obviously be calc'ing all the uprights w/in the design area, but what about the pendent's in the clouds? Do I calc all the ceiling cloud heads w/in the DA? Two heads? Thanks, Bob Knight (208) 639-8790 Direct Phone (208) 639-8791 Direct Fax (208) 994-1439 Cell _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)