NFPA 25 2011 13.4.4.2 is the section you want, the Annual trip test with the valve partially open and a full flow trip test every 3 years. 5.3.3.5 only applies to the waterflow alarm testing (EG the pressure switch which is quarterly). Mike Morey, SET Sprinkler Designer BMW Constructors, Inc. O: 317.651.0596 | C: 317.439.2695 www.bmwc.com <https://owa.bmwc.com/exchweb/bin/redir.asp?URL=http://www.bmwc.com>
________________________________ From: [email protected] on behalf of Ed Kramer Sent: Thu 3/31/2011 1:19 PM To: [email protected] Subject: RE: dry system trip test connection I just did quick look-over of NFPA 25 (2011) on the NFPA website. Section 5.3.3.5 says that testing dry system waterflow alarms SHALL be done using the bypass connection (not the remote trip test connection). What needs to be done at least every year that involves the trip test connection? Ed Kramer > -----Original Message----- > From: [email protected] [mailto:sprinklerforum- > [email protected]] On Behalf Of Ron Greenman > Sent: Thursday, March 31, 2011 11:15 AM > To: [email protected] > Subject: Re: dry system trip test connection > > Yes. At least every year. > > On Thu, Mar 31, 2011 at 9:46 AM, Ed Kramer <[email protected]> wrote: > > I'm not NFPA 25 knowledgeable - hope someone can clue me in. > > > > > > > > After the initial acceptance test, does the dry system trip test > connection > > ever get used again? > > > > > > > > Ed Kramer > > > > Littleton, CO > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > For Technical Assistance, send an email to: [email protected] > > > > To Unsubscribe, send an email to:Sprinklerforum- > [email protected] > > (Put the word unsubscribe in the subject field) > > > > > > -- > Ron Greenman > Instructor > Fire Protection Engineering Technology > Bates Technical College > 1101 So. Yakima Ave. > Tacoma, WA 98405 > > [email protected] > > http://www.bates.ctc.edu/fireprotection/ > > 253.680.7346 > 253.576.9700 (cell) > > Member: > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC > > They are happy men whose natures sort with their vocations. -Francis > Bacon, essayist, philosopher, and statesman (1561-1626) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:Sprinklerforum- > [email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)