Oops, you are correct, I forgot I'm reading the non-handbook version since the 
handbook isn't out yet (I'm used to the annexes being on the same page).
 
Mike Morey, SET
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.439.2695
www.bmwc.com 
<https://owa.bmwc.com/exchweb/bin/redir.asp?URL=http://www.bmwc.com> 
 

________________________________

From: [email protected] on behalf of Ed Kramer
Sent: Thu 3/31/2011 2:34 PM
To: [email protected]
Subject: RE: dry system trip test connection



Section A.13.4.4.2.2.3 suggests that bleeding air at the dry valve is
acceptable for a partial flow trip test.  If I'm reading that correctly, the
trip test valve should only be needed every 3 years.  Am I missing
something?

Ed Kramer