Section A.13.4.4.2.2.3 suggests that bleeding air at the dry valve is
acceptable for a partial flow trip test.  If I'm reading that correctly, the
trip test valve should only be needed every 3 years.  Am I missing
something?

Ed Kramer

> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of Morey, Mike
> Sent: Thursday, March 31, 2011 12:16 PM
> To: [email protected]
> Subject: RE: dry system trip test connection
> 
> Just to clarify, the trip test valve will be used yearly, 2 of the 3
> years are a "partial" trip test where you need only leave the supply
> valve cracked open.  The reasoning is this tests the valve's actuation
> without filling the entire system with water, generally you just fill
> the riser pipe as long as your quick to shut it off (prevents you from
> having to drain all the low points etc).  The quarterly tests of the
> water flow alarm are the only test that may be done with the air bleed,
> the annual test is designed to test the funcionality of the valve, where
> the quarterly test focuses only on the alarm device itself.
> 
> Mike Morey, SET
> Sprinkler Designer
> BMW Constructors, Inc.
> O: 317.651.0596 | C: 317.439.2695
> www.bmwc.com
> <https://owa.bmwc.com/exchweb/bin/redir.asp?URL=http://www.bmwc.com>
> 
> 
> ________________________________
> 
> From: [email protected] on behalf of Ed Kramer
> Sent: Thu 3/31/2011 2:08 PM
> To: [email protected]
> Subject: RE: dry system trip test connection
> 
> 
> 
> Thank you Ron, Tom and Mike.
> 
> Looks like the trip test valve is used at least every 3 years, and as
> often
> as every year if air can't be bled off at the dry valve.
> 
> Ed Kramer
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to